This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Mapped modbus objects value issue
#4
Most of your object log entries are group reads which don't have a value.

In one of the screenshots a device is marked in red meaning that there's a communication issue. Check Error log in the Modbus tab for more details. Usually communication errors are fixed when GND is connected between LM and all other Modbus devices.