This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus write error
#1
Hello,
I have a problem. I updated genohm-scada-modbus package version 20230404 to 20240621 and FW version 20230607 to 20240426. Now I run a write command and I get this error: "Write failed: Illegal data value". The only change in Modbus profile is to add write_delay:1 in the file header. I also tried package 20231213 and I have the same error. The error doesn't always occur, ometimes write correctly. It is possible to know which mapping element triggers the error?

Code:
{   "manufacturer": "TEST",   "description": "Modbus",   "timeout": 5,   "read_swap": "n",    "write_delay":1,   "mapping": [         {"name": "Allow Heating_[R/W]",     "bus_datatype": "bool",     "type": "register",     "datatype": "uint16",     "address": 47371,     "writable": 1,     "write_multiple": 1,     "read_count": 1,     "value_delta": 1,     "value_multiplier": 1,     "value_custom": {             "0": "Off",             "1": "On"             }          },     {"name": "Allow Cooling_[R/W]",     "bus_datatype": "bool",     "type": "register",     "datatype": "uint16",     "address": 47372,     "writable": 1,     "write_multiple": 1,     "read_count": 1,     "value_delta": 1,     "value_multiplier": 1,     "value_custom": {             "0": "Off",             "1": "On"             }              } ]}
Reply


Messages In This Thread
Modbus write error - by didac - 11.02.2025, 11:37
RE: Modbus write error - by Daniel - 11.02.2025, 11:46
RE: Modbus write error - by didac - 11.02.2025, 13:49
RE: Modbus write error - by admin - 11.02.2025, 13:53
RE: Modbus write error - by didac - 11.02.2025, 13:59
RE: Modbus write error - by Daniel - 11.02.2025, 14:01
RE: Modbus write error - by didac - 11.02.2025, 14:12
RE: Modbus write error - by admin - 12.02.2025, 06:55
RE: Modbus write error - by didac - 12.02.2025, 09:08
RE: Modbus write error - by admin - 12.02.2025, 09:12