30.04.2025, 07:47
It seems you just need to keep 1102 as a value 1 to accept values to 1099, write 1 to 1102 before. Setpoint should be uint16
------------------------------
Ctrl+F5
Ctrl+F5
Issue Writing Setpoint on Modbus Device (PLOGIC)
|