This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus connection problem LG Energy Storage System
#8
Fault:
Use Value bitmask option. Click the calculator icon to select the required bits. Set Modbus data type to uint32 and Object data type to 1 bit.

Active power:
Modbus register datatype = uint32
Object datatype = 14. 4 byte floating point
Value multiplier (advanced settings) = 0.01
Reply