It is probably in hex, slave 11, 12, 13, 14. Disable the script from admin, set the RTU mode as per this document and use Read test under modbus tab
Device address 11, holding register and try different addresses: 2, 3, 40002, 40003.
see what happens.
Device address 11, holding register and try different addresses: 2, 3, 40002, 40003.
see what happens.
------------------------------