This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus profile of LM internally supports ONLY uint16 registers without type switchin
#5
Hello, I was able to solve the problem. My mistake was that I modified and saved an existing profile. However, it is important to export it and import it again. Then it works.

I also compared the old and the new .json scripts. The main problem was the distinction between bus data type and interpretation data type. Internally, LM distinguishes between the bus data type (how it is read) and the interpretation data type (how it is evaluated). In my profile, this was either mixed up or not present at all.

So thank you and the Modbus profiler app is a great help for such specific cases.
Reply


Messages In This Thread
RE: Modbus profile of LM internally supports ONLY uint16 registers without type switchin - by Streety - 20.12.2025, 07:27