You can't use a profile because this is a custom protocol not Modbus.
For testing purposes use an event script. Change baudrate, parity and command bytes as needed.
If the test script works then it can be modified to send different commands depending on the input value. 4-bit value should work (e.g. up/down/stop).
For testing purposes use an event script. Change baudrate, parity and command bytes as needed.
Code:
require('serial')
port = serial.open('/dev/RS485-1', {
baudrate = 9600,
parity = 'even',
duplex = 'half'
})
command = string.char(0x55, 0x01, 0x01, 0x03, 0x02, 0xF9, 0x01)
port:write(command)If the test script works then it can be modified to send different commands depending on the input value. 4-bit value should work (e.g. up/down/stop).