This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Schneider RMH modbus
#4
First, make sure that all properties are in lower case or it will not work (you have Value_bitmask).
Correct address for Alarm status is 201 (202 - 1 = 0xC9), there's no NaN value there. It's a single register, so datatype is not needed, bus datatype must be Boolean.
{"bus_datatype":"bool","bus_address":27654,"address":201,"value_bitmask":0x01,"type":"register","name":"Channel 1"}