Mail from Rithum: Each Rithum Switch uses one TP connection to an IP Gateway, in this case your LogicMachine. This connection is persistent.
Most KNX gateways publish the number of concurrent connections they can support, but I can't see that published anywhere for the LogicMachine. ETS uses the same mechanism, so if your gateway only supports one connection, that is what the issue is.
The Weinzierl 732, for example, supports up to 8 connections.
How many connections are supported by the LogicMachine?
Most KNX gateways publish the number of concurrent connections they can support, but I can't see that published anywhere for the LogicMachine. ETS uses the same mechanism, so if your gateway only supports one connection, that is what the issue is.
The Weinzierl 732, for example, supports up to 8 connections.
How many connections are supported by the LogicMachine?