This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

BACNET IP and IP filters comm
#18
based on the group monitor 1.2.250 sends read request to 0/0/28, you must find it out what does it. Its ether parameter on object or script.
------------------------------
Ctrl+F5
Reply


Messages In This Thread
BACNET IP and IP filters comm - by ALEJANDRO - 31.03.2026, 10:09
RE: BACNET IP and IP filters comm - by admin - 31.03.2026, 10:27
RE: BACNET IP and IP filters comm - by admin - 31.03.2026, 11:02
RE: BACNET IP and IP filters comm - by admin - 14.04.2026, 13:00
RE: BACNET IP and IP filters comm - by Daniel - 14.04.2026, 15:29
RE: BACNET IP and IP filters comm - by admin - 15.04.2026, 07:20
RE: BACNET IP and IP filters comm - by admin - 15.04.2026, 07:57
RE: BACNET IP and IP filters comm - by Daniel - 15.04.2026, 08:08
RE: BACNET IP and IP filters comm - by Daniel - 15.04.2026, 08:56
RE: BACNET IP and IP filters comm - by Daniel - 15.04.2026, 09:09
RE: BACNET IP and IP filters comm - by Daniel - 15.04.2026, 09:16
RE: BACNET IP and IP filters comm - by Daniel - 15.04.2026, 09:37
RE: BACNET IP and IP filters comm - by Daniel - 15.04.2026, 10:18
RE: BACNET IP and IP filters comm - by admin - 15.04.2026, 10:39
RE: BACNET IP and IP filters comm - by admin - 15.04.2026, 11:07
RE: BACNET IP and IP filters comm - by Daniel - 16.04.2026, 14:04
RE: BACNET IP and IP filters comm - by Daniel - 16.04.2026, 14:16
RE: BACNET IP and IP filters comm - by Daniel - 16.04.2026, 14:49
RE: BACNET IP and IP filters comm - by Daniel - 16.04.2026, 16:11
RE: BACNET IP and IP filters comm - by admin - 22.04.2026, 11:57
RE: BACNET IP and IP filters comm - by admin - 22.04.2026, 13:56
RE: BACNET IP and IP filters comm - by admin - 27.04.2026, 12:05
RE: BACNET IP and IP filters comm - by Daniel - 27.04.2026, 12:19
RE: BACNET IP and IP filters comm - by admin - 27.04.2026, 12:19
RE: BACNET IP and IP filters comm - by admin - 27.04.2026, 14:20
RE: BACNET IP and IP filters comm - by admin - 28.04.2026, 06:21
RE: BACNET IP and IP filters comm - by Daniel - 28.04.2026, 07:13
RE: BACNET IP and IP filters comm - by Daniel - 28.04.2026, 13:41
RE: BACNET IP and IP filters comm - by Daniel - 30.04.2026, 08:18
RE: BACNET IP and IP filters comm - by Daniel - 30.04.2026, 08:46
RE: BACNET IP and IP filters comm - by Daniel - 30.04.2026, 08:58
RE: BACNET IP and IP filters comm - by Daniel - 30.04.2026, 09:02

Forum Jump: