This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Visu localbus.js reconnect behaviour, reuse object registry, reconnect without delay
#3
You're right — with a WebSocket-only reconnect, changes that happen while the socket is down are not re-synced. Let me correct the proposal: keep the value resync, but make it incremental.

Your legacy visualization already does exactly this: POST /scada-vis/objects/ws with "updatetime" returns only the objects changed since that time. Measured on 20251204 with 2832 objects: 14 bytes / 39 ms when nothing changed, 90 KB with updatetime=0.

Could /apps/localbus.lp accept the same "updatetime" parameter (the last tsec the client received), or could the WebSocket send a catch-up of changes since that time on open? Then the client can reopen the socket immediately and fetch only the delta: no data loss, no fixed 1 s wait, no 285 KB per reconnect.

Until then, on our side we will reopen the socket first and run the full POST in the background, merging by updatetime, so live data resumes within ~25 ms and consistency is restored when the POST completes.