This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Possible bug in modbus reading
#6
Looks like the device has a low limit of open connections. Enable persistent mode in Modbus tab / device settings and try again. You might need to power cycle the device so it will start accepting connections faster.