21.07.2017, 18:34
Buudzik,
I think that from this table you only need the PrVal identifier (called Current value here). It has values 0-3 which equals to Low-Middle-High-Stop - and it's read only.
The other identifiers are not necessary from this bacnet object. You should find another datapoint that can be used to control the device. Use Yabe to find the needed points.