This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus read upper/lower word
#2
Are you using profile or scripts? For profiles you have to set datatype field to "uint32", otherwise use mb:readregistervalue(0x1A, "uint32", "w"). You might also need to adjust read_swap parameter. Start with reading the value from RTU read test in modbus tab.
Reply