This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

F&F LE-03MQ Modbus energy counter
#11
(22.09.2017, 20:09)Erwin van der Zwart Wrote: Hi,

Registers are always 16 bits, so float32 is divided over 2 registers, please try type input register (function code 4 according to manual)

BR,

Erwin

Yes, this was the cause, but for the frequency this is not solution, but I will be 100% confident when I will tomorrow connect counter as should be because now it is only connected to 1 phase and frequency is the parameter of all 3 phases so it could be the cause of this second issue. Thanks Erwin, you're the bestWink

After a few minutes, register starts respond. A little strange but true. But still there are some errors in communication(timeout errors).