Hi,
1) No i checked this in the ETS monitor and the value is a 6 byte value like $0C $D2 $0C $D3 $0D $C2 and not like $00 $00 .. $0C $D2 $0C $D3 $0D $C2 so all unused bytes in the 255 bytes are not send at all, making it a valid value (in 222.100 format) for your 6 byte object.
2) Because you send the value from KNX to the 6 byte it will only repond to split it to 3 bytes when it's from KNX and not when comming from local source (not from spaceLYnk), when you update the 255 byte object by the write from BACnet action it normaly would split the values again and create a loop, now it doesn't (:
BR,
Erwin
1) No i checked this in the ETS monitor and the value is a 6 byte value like $0C $D2 $0C $D3 $0D $C2 and not like $00 $00 .. $0C $D2 $0C $D3 $0D $C2 so all unused bytes in the 255 bytes are not send at all, making it a valid value (in 222.100 format) for your 6 byte object.
2) Because you send the value from KNX to the 6 byte it will only repond to split it to 3 bytes when it's from KNX and not when comming from local source (not from spaceLYnk), when you update the 255 byte object by the write from BACnet action it normaly would split the values again and create a loop, now it doesn't (:
BR,
Erwin