22.10.2017, 11:03
(This post was last modified: 22.10.2017, 11:07 by Monolithos.)
Since the last update of mosaic (FW 20170620), I find it suits a lot of basic visualisation needs so I tend to use it more and more
But (ain't there always...), I'm currently doing a mosaic visualisation using also the Mosaic thermostat widgets and found it has 1) a bug and 2) it is not completely KNX HVAC mode compliant.
1) the bug : when receiving the status object for KNX HVAC mode (as a 1 byte object DPT 05) 3 (Night reduction) or 4 (Builing protection), the script behind the widget apparently distracts 1 from the value and shows the wrong icon on the mosaic thermostat (Building protection shows as Night reduction and Night reduction shows as Standby (Eco) mode.
No object values are changed and no bus traffic, just an internal visualisation error but of course confusing for the user.
2) Best practices for KNX HVAC mode (via dpt 20.102) implementation is to use an offset of the basic comfort setpoint temperature to define Standby and Night reduction modes.
Also, an offset is to be used to alter the comfort setpoint temperature.
The mosaic widget only supports theĀ changing (and visualisation) of a 2 byte object while the KNX HVAC offset is a 1 bit signed object (dpt 06.010).
As a result, in order to change the setpoint temperature, you now need to change the basic comfort setpoint temperature, involuntarily also changing the values for Standby and Night Reduction.
It would be very nice if the thermostat would support the complete KNX HVAC mode scenario
Kind regards,
Hendrik
Kind regards,
Hendrik