This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Error log - Modbus
#9
Hi,

EOL termination means placing a resistor parallel over the "end of line", this is required by the Modbus standard to avoid reflections but when using just a 1m cable i don't think it will make a difference.

Are you sure the RS485 port is not called from another process? (like from modbus template and also from script), did you try to restart the controller to be sure there is no old script still loaded?

If that is not the case then i would suggest to test with a new cable between the meter and controller, i would use 2 x 0.8 ..

BR,

Erwin
Reply


Messages In This Thread
Error log - Modbus - by Mr.D - 24.01.2018, 18:15
RE: Error log - Modbus - by admin - 25.01.2018, 07:27
RE: Error log - Modbus - by Mr.D - 25.01.2018, 08:06
RE: Error log - Modbus - by Daniel - 25.01.2018, 12:00
RE: Error log - Modbus - by Mr.D - 25.01.2018, 16:49
RE: Error log - Modbus - by Daniel - 25.01.2018, 16:54
RE: Error log - Modbus - by Mr.D - 25.01.2018, 19:51
RE: Error log - Modbus - by Erwin van der Zwart - 25.01.2018, 22:50
RE: Error log - Modbus - by Mr.D - 27.01.2018, 12:17
RE: Error log - Modbus - by Mr.D - 28.01.2018, 09:55
RE: Error log - Modbus - by Mr.D - 29.01.2018, 18:46
RE: Error log - Modbus - by Mr.D - 29.01.2018, 20:25
RE: Error log - Modbus - by SigmaTec - 01.02.2018, 17:09
RE: Error log - Modbus - by Mr.D - 13.03.2018, 13:07
RE: Error log - Modbus - by sx3 - 18.04.2018, 12:01
RE: Error log - Modbus - by mlaudren - 18.04.2018, 21:50
RE: Error log - Modbus - by iJAF - 17.07.2019, 11:48

Forum Jump: