This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

ModBus on SL/HL/W - Mislabelling?
#2
Both are correct Smile
Numbering in your doc refers to "traditional numbering standard", while RTU read test uses Modbus function number. For some historical reason address numbering and function numbers for registers are swapped. Keep in mind that actual registers are numbered from 0, not from 1 as specified in your doc.
Reply