Check to which priority array your scada is writing to. LM by default will write to 16 but you can change it. If your scada is writing to higher priority then yes it will be overridden and all values from LM will be in PA16 but ignored by Present Value.
Yo can clear priority array on LM by simply disabling bacnet server and enabling it again.
First exported 256 objects will have COV. If you have more then the rest must be pooled. Proper bacnet client will just deal with it out of the box.
BR