15.02.2018, 19:00
I was on site today, and did some tests.
When I disabled/enabled the LM, the bacnet-objects status flags were set to 0. But at the first update of the objects on knx-bus the "overridden" got set to 1.
This is a read tag in the scada, so there is no writing to this objects. Only updated on the knx.
There are also differse between the value in the priority array 16 and the present value property of the bacnet-object.
Also tested with YABE(yet another bacnet scanner) and wago bacnet configurator with the same result.
I had the support from the scada-developer to have a quick look also, and they checked with wireshark.
The status-flags appeared to be set from the lm5.
Could anyone help me with this issue?
Eirik
When I disabled/enabled the LM, the bacnet-objects status flags were set to 0. But at the first update of the objects on knx-bus the "overridden" got set to 1.
This is a read tag in the scada, so there is no writing to this objects. Only updated on the knx.
There are also differse between the value in the priority array 16 and the present value property of the bacnet-object.
Also tested with YABE(yet another bacnet scanner) and wago bacnet configurator with the same result.
I had the support from the scada-developer to have a quick look also, and they checked with wireshark.
The status-flags appeared to be set from the lm5.
Could anyone help me with this issue?