18.02.2018, 15:09
Hi
Here's an update about the bacnet.
I've testet the bacnet on another prosject and discovered some strange behavior also on these two LM5's.
On this project I've didn't connect with my SCADA-system, but with two different bacnet-clients.
The Wago Bacnet-configurator and the Yet Another Bacnet Scanner.
When scanning and connecting to the LM5 then some objects returned with these properties:
Relingiush default returned the same value as the present value.
When trying to change/write to this property the "write access denied" came back.
On an update on the present value property the overridden status flag return "1".
On this project the bacnet-server has been disabled and not integrated in other systems earlier.
And are there any other programs I could use to test with?
Have been testing with 3 different clients with the same result.
Are there any difference in the bacnet integration on LM5, Spacelynk or Wiser.....?
Eirik
Here's an update about the bacnet.
I've testet the bacnet on another prosject and discovered some strange behavior also on these two LM5's.
On this project I've didn't connect with my SCADA-system, but with two different bacnet-clients.
The Wago Bacnet-configurator and the Yet Another Bacnet Scanner.
When scanning and connecting to the LM5 then some objects returned with these properties:
Relingiush default returned the same value as the present value.
When trying to change/write to this property the "write access denied" came back.
On an update on the present value property the overridden status flag return "1".
On this project the bacnet-server has been disabled and not integrated in other systems earlier.
And are there any other programs I could use to test with?
Have been testing with 3 different clients with the same result.
Are there any difference in the bacnet integration on LM5, Spacelynk or Wiser.....?
Eirik