This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus Schneider PLCs
#2
All JSON keys must be lowercase, but you have Read_count and Read_offset. read_count must be 6, it is counted in 16-bit registers so 2 x 3 in your case. Also, you are probably missing "datatype": "float32" for each profile entry.