This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

read failed: Illegal data address
#1
Hello,

I'm trying to make a JSON mapper for the Schneider APC UPS ove Modbus TCP but I'm having some problems.
No values get present, and the error is: read failed: Illegal data address

This is what I have mapped up so far:
Code:
{
 "manufacturer": "Schneider",
 "description": "APC UPS",
 "mapping": [
 { "name": "On Line", "bus_datatype": "bool", "type": "register", "address": 3, "writable": 0, "value_bitmask": 0x8, "bus_address": "6/0/0" },
 { "name": "On battery", "bus_datatype": "bool", "type": "register", "address": 3, "writable": 0, "value_bitmask": 0x10, "bus_address": "6/0/1" },
{ "name": "Overload", "bus_datatype": "bool", "type": "register", "address": 3, "writable": 0, "value_bitmask": 0x20, "bus_address": "6/0/2" },
{ "name": "Low battery", "bus_datatype": "bool", "type": "register", "address": 3, "writable": 0, "value_bitmask": 0x40, "bus_address": "6/0/3" },
{ "name": "Replace battery", "bus_datatype": "bool", "type": "register", "address": 3, "writable": 0, "value_bitmask": 0x80, "bus_address": "6/0/4" },
{ "name": "% battery state of charge", "bus_datatype": "float16", "type": "register", "address": 5, "writable": 0, "bus_address": "6/0/5" },
{ "name": "Runtime remaining", "bus_datatype": "float16", "type": "register", "address": 6, "writable": 0, "bus_address": "6/0/6" },
{ "name": "Battery voltage", "bus_datatype": "float16", "type": "register", "address": 7, "writable": 0, "bus_address": "6/0/7" },
{ "name": "UPS internal temperature", "bus_datatype": "float16", "type": "register", "address": 8, "writable": 0, "bus_address": "6/0/8" },
{ "name": "Amps drawn by load", "bus_datatype": "float16", "type": "register", "address": 9, "writable": 0, "bus_address": "6/0/9" },
{ "name": "Quantity of bad batt packs", "bus_datatype": "float16", "type": "register", "address": 10, "writable": 0, "bus_address": "6/0/10" },
{ "name": "Quantity of batt packs", "bus_datatype": "float16", "type": "register", "address": 11, "writable": 0, "bus_address": "6/0/11" },
{ "name": "% power drawn by load", "bus_datatype": "float16", "type": "register", "address": 12, "writable": 0, "bus_address": "6/0/12" },
{ "name": "Nominal power output", "bus_datatype": "float16", "type": "register", "address": 13, "writable": 0, "bus_address": "6/0/13" },
{ "name": "Actual output voltage", "bus_datatype": "float16", "type": "register", "address": 14, "writable": 0, "bus_address": "6/0/14" },
{ "name": "Maximum input", "bus_datatype": "float16", "type": "register", "address": 15, "writable": 0, "bus_address": "6/0/15" },
{ "name": "Minimum input", "bus_datatype": "float16", "type": "register", "address": 16, "writable": 0, "bus_address": "6/0/16" },
{ "name": "Input voltage", "bus_datatype": "float16", "type": "register", "address": 17, "writable": 0, "bus_address": "6/0/17" },
{ "name": "Input frequency", "bus_datatype": "float16", "type": "register", "address": 18, "writable": 0, "bus_address": "6/0/18" },
{ "name": "Low battery duration", "bus_datatype": "float16", "type": "register", "address": 31, "writable": 0, "bus_address": "6/0/19" }


 ]
}

This is the documentation regarding Modbus protocol for the UPS:
http://download.schneider-electric.com/f..._R1_EN.pdf

Is it something with hexadecimal/decimal adresses? or with my bitmasking?
The documentations states UINT16 on datatype, must I add this to the mapper?