This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus profie Satec PM130 Plus
#7
(27.01.2016, 16:49)admin Wrote: It might have different register/byte order. Try reading registers 13342 and 13343 as uint16 and post what values you get here.

I think the problem is not reading Modbus register 13342 as int32. May be the value going wrong when transfer it to 4 byte knx variable.

Attached Files Thumbnail(s)
   