This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

TP Repeats
#8
(02.07.2018, 10:52)AEK Wrote:
(30.06.2018, 11:03)iridium Wrote:
(29.06.2018, 07:53)admin Wrote: Repeats are probably coming from scripts that use grp.write to a group address that is not assigned to a real KNX device. You should either use virtual objects or grp.update in this case.

Thanks!!
I Will check It!

also, if you have only sensor in line w/o any actors you will have the same problem.
in that case you can activate "ACK all group telegrams" option in network - knx connection menu

Yes!! that was the problem!
Thank you
Reply