Read/write does not really matter, but the you should have all read/write operations in a single script. This is due to BACnet using one port for both client and server so parallel requests are not supported.
I can't guarantee that 1000 objects will work without large delays. Client is mostly meant for several tens of objects. Maybe you can use ModBus TCP on your PLCs? This way you can use one script be PLC and run everything in parallel. There's no advantage in using BACnet because values have to be polled anyway.
I can't guarantee that 1000 objects will work without large delays. Client is mostly meant for several tens of objects. Maybe you can use ModBus TCP on your PLCs? This way you can use one script be PLC and run everything in parallel. There's no advantage in using BACnet because values have to be polled anyway.