This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Systemair RS-485
#4
The ventilation system is a modbus slave. In the manual the Master is an indication of were the line termination should be. And the master will be your LM.
Your unit is indicated by the RJ45 plugs, Position 2 on page 4.

The setup you have set, has this been setup the same way on the LM? I am reading a Flexit unit from my LM, and have set up Half-Duplex on it and the same parameters as set on the unit.
Reply