There is no one secret answer but in short this info comes directly from the TP UART chip. In most cases this will happen when there will be lots of telegrams at the same time. Good practice is to check your scripts and make sure they write to TP only when necessary. Use grp.update when TP is not needed and grp.checkwrite when writing to TP to not write the same value all over again. Apply filter if you use more then one IP router.
BR
There is no one secret answer but in short this info comes directly from the TP UART chip. In most cases this will happen when there will be lots of telegrams at the same time. Good practice is to check your scripts and make sure they write to TP only when necessary. Use grp.update when TP is not needed and grp.checkwrite when writing to TP to not write the same value all over again. Apply filter if you use more then one IP router.