04.07.2019, 15:32
(This post was last modified: 04.07.2019, 15:33 by Erwin van der Zwart.)
Hi,
There is indeed a new gateway but the system registers are not changed in this new gateway. This does not change any register in the powertag itself.
We have entered the most used registers in the profile and we could add a few more as they already excisted in the powertag device.
Here is the register list of both (system gateway and powertag) See page 66 for the system registers to be read on slave ID 255 and page 68 for the powertag registers to be read at slave ID ### depending on the selected powertag.
BR,
Erwin
There is indeed a new gateway but the system registers are not changed in this new gateway. This does not change any register in the powertag itself.
We have entered the most used registers in the profile and we could add a few more as they already excisted in the powertag device.
Here is the register list of both (system gateway and powertag) See page 66 for the system registers to be read on slave ID 255 and page 68 for the powertag registers to be read at slave ID ### depending on the selected powertag.
DOCA0157EN-00.pdf (Size: 5.02 MB / Downloads: 43)
BR,
Erwin