This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Bacnet status flags
#40
(15.02.2018, 19:22)Erwin van der Zwart Wrote: Hi,

I have seen this once before on a Sauter BMS, also on the read values, what Sauter did was showing the override flag when the value in the prio array was higher then the relinquish default value.

Because the values where read only we have set the relinquish default value to the max object value and that solved the issue. Personally i don’t think it is a issue on our side but on the BMS side, our own Ecostruxure Building Operation BMS has no issues with this.

BR,

Erwin

Where did you change this value? I am having the same issue in a different project. 

T
There are 10 kinds of people in the world; those who can read binary and those who don't  Cool
Reply


Messages In This Thread
Bacnet status flags - by eirik - 14.02.2018, 07:45
RE: Bacnet status flags - by Daniel - 14.02.2018, 08:33
RE: Bacnet status flags - by eirik - 14.02.2018, 09:06
RE: Bacnet status flags - by Daniel - 14.02.2018, 09:10
RE: Bacnet status flags - by eirik - 15.02.2018, 19:00
RE: Bacnet status flags - by Daniel - 15.02.2018, 19:06
RE: Bacnet status flags - by Trond Hoyem - 13.05.2020, 11:04
RE: Bacnet status flags - by eirik - 15.02.2018, 21:24
RE: Bacnet status flags - by Daniel - 15.02.2018, 22:33
RE: Bacnet status flags - by eirik - 16.02.2018, 07:05
RE: Bacnet status flags - by eirik - 18.02.2018, 15:09
RE: Bacnet status flags - by Daniel - 18.02.2018, 16:26
RE: Bacnet status flags - by eirik - 18.02.2018, 17:23
RE: Bacnet status flags - by admin - 18.02.2018, 18:57
RE: Bacnet status flags - by eirik - 19.02.2018, 06:14
RE: Bacnet status flags - by admin - 19.02.2018, 07:07
RE: Bacnet status flags - by eirik - 19.02.2018, 08:06
RE: Bacnet status flags - by eirik - 19.02.2018, 13:40
RE: Bacnet status flags - by admin - 19.02.2018, 13:50
RE: Bacnet status flags - by admin - 19.02.2018, 14:22
RE: Bacnet status flags - by Livadi77 - 16.03.2018, 16:40
RE: Bacnet status flags - by Tokatubs - 08.04.2019, 07:23
RE: Bacnet status flags - by Livadi77 - 15.04.2019, 14:14
RE: Bacnet status flags - by domotiqa - 16.10.2019, 18:41
RE: Bacnet status flags - by Livadi77 - 17.10.2019, 05:53
RE: Bacnet status flags - by Daniel - 15.04.2019, 14:18
RE: Bacnet status flags - by Livadi77 - 18.04.2019, 20:54
RE: Bacnet status flags - by Livadi77 - 14.05.2020, 06:58
RE: Bacnet status flags - by stavros - 12.09.2019, 08:27
RE: Bacnet status flags - by Polkaz - 23.05.2019, 18:45
RE: Bacnet status flags - by Daniel - 12.09.2019, 08:49
RE: Bacnet status flags - by domotiqa - 17.10.2019, 11:16
RE: Bacnet status flags - by domotiqa - 25.10.2019, 06:10

Forum Jump: