This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

BACnet unit type
#4
Hi,

The fact that ASHRAE has specified something does not automatically means it is implemented.

Manufacturers have a lot of freedom in BACnet even if a product is BTL listed.

For a BACnet object there are only 3 properties mandatory and those are ID, Name and Type all other properties are optional including the property Unit.

Nice thing to notice is that even the Value property is optional (:

The Unit property is not existing in the BACnet objects that are hosted by the controller.

BR,
Erwin