This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Bacnet Server
#2
Hi,

I guess you restarted the controller as you mentioned ‘read during startup’

I don’t think that enabling that parameter had anything to do with your issue...

Restarting is causing the priority array to be cleared and i think your issue is that you wrote a value in the array at a higher level then the default 16.

If you write any value at a higer prio in the array then this value is overruling the values comming from the GA.

What is the default prio in your 3th party software? I see some manufacturers using 10 as default.

Try to change a value from the client side, and check if it sets the value in the prio array at a higher level then 16.

BR,

Erwin
Reply


Messages In This Thread
Bacnet Server - by Tokatubs - 04.04.2019, 21:16
RE: Bacnet Server - by Erwin van der Zwart - 05.04.2019, 05:32
RE: Bacnet Server - by Tokatubs - 05.04.2019, 08:49
RE: Bacnet Server - by admin - 05.04.2019, 09:19
RE: Bacnet Server - by Tokatubs - 05.04.2019, 09:45
RE: Bacnet Server - by eirik - 05.04.2019, 18:46
RE: Bacnet Server - by Tokatubs - 06.04.2019, 20:56
RE: Bacnet Server - by Tokatubs - 09.04.2019, 08:08
RE: Bacnet Server - by Daniel - 09.04.2019, 08:21
RE: Bacnet Server - by Tokatubs - 09.04.2019, 10:21
RE: Bacnet Server - by admin - 09.04.2019, 08:29
RE: Bacnet Server - by Tokatubs - 09.04.2019, 09:01
RE: Bacnet Server - by admin - 09.04.2019, 09:37
RE: Bacnet Server - by admin - 09.04.2019, 10:33
RE: Bacnet Server - by Tokatubs - 10.04.2019, 09:43

Forum Jump: