This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

EnOcean profile A5-20-01
#6
(21.11.2019, 07:50)admin Wrote: This is a separate script not a profile. You need to use RAW profile in EnOcean tab. Script handles parsing of RAW value.
It's all explained in the header of the script (:

Line 100 is not a error, this is not a update to the drive status value but a KNX value update command, i use grp.update on purpose as i don't see any reason to post feedback to the KNX bus, if you need it on KNX then you should change it to grp.write

Yes you need a seperate event based script for each drive, so if you have 10 drives you need 20x 4 byte objects and 10x event based scripts, each event script is attached to the Enocean incomming 4 byte RAW value, and you need to set 10x the response 4 byte object to Enocean Outgoing.  The addresses needs to be matched to the objects you create...

BR,

Erwin