This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus values wrong
#10
You might need to uncomment setslave() call and set correct slave id like this:
Code:
mb:setslave(1)
You can also run Wireshark on your PC together with Modbus Poll to see raw communication. This might help to find out correct settings.