This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

LM und Daikin RTD-W - Modbus
#29
My profile now looks like this - should it be describable, right? So far nothing has changed!
sri, but i am more than grateful for your help!

Enclosed the profile.


Code:
{
  "product_code": "RT",
  "manufacturer": "Realtime",
  "name": "RTD-W Control",
  "product_range": "Realtime Modbus",
  "description": "Realtime Modbus RT ",
  "mapping": [
    {
      "name": "Sollwert Wasservorlauf Heizen",
      "address": 1,
      "bus_datatype": 9,
      "datatype": "uint16",
      "type": "register",
      "value_multiplier": "0.01",
      "writable": 1
    },
    {
      "name": "Sollwert Wasservorlauf Kuehlen",
      "address": 2,
      "bus_datatype": 9,
      "datatype": "uint16",
      "type": "register",
      "value_multiplier": "0.01",
      "writable": 1
    },
    {
      "name": "Sensoreingang Heizen ein",
      "address": 10001,
      "bus_datatype": 1,
      "datatype": "int16",
      "type": "register",
      "writable": 1
     }
  ]
}
Reply


Messages In This Thread
LM und Daikin RTD-W - Modbus - by mkoermer - 19.10.2020, 07:20
RE: LM und Daikin RTD-W - Modbus - by admin - 19.10.2020, 08:32
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 08:49
RE: LM und Daikin RTD-W - Modbus - by alexll - 19.10.2020, 09:55
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 10:13
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 10:34
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 10:57
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 11:26
RE: LM und Daikin RTD-W - Modbus - by admin - 19.10.2020, 11:27
RE: LM und Daikin RTD-W - Modbus - by admin - 19.10.2020, 11:32
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 11:42
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 11:51
RE: LM und Daikin RTD-W - Modbus - by admin - 19.10.2020, 11:54
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 11:55
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 12:36
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 12:43
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 12:55
RE: LM und Daikin RTD-W - Modbus - by mkoermer - 19.10.2020, 13:46
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 13:49
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 13:57
RE: LM und Daikin RTD-W - Modbus - by Daniel - 19.10.2020, 13:59

Forum Jump: