This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus TCP HVAC Gateway
#9
The example assumes that the product type and indoor unit address are both 0.
You can calculate coil/register address using this formula (point number is from the table that you have provided where addressing starts from 1):
address = TYPE * 4096 + UNIT_ADDR * 16 + POINT - 1
Reply


Messages In This Thread
Modbus TCP HVAC Gateway - by KoBra - 02.11.2020, 08:45
RE: Modbus TCP HVAC Gateway - by Daniel - 02.11.2020, 08:47
RE: Modbus TCP HVAC Gateway - by admin - 02.11.2020, 08:51
RE: Modbus TCP HVAC Gateway - by KoBra - 02.11.2020, 09:34
RE: Modbus TCP HVAC Gateway - by admin - 02.11.2020, 09:40
RE: Modbus TCP HVAC Gateway - by KoBra - 02.11.2020, 10:32
RE: Modbus TCP HVAC Gateway - by KoBra - 18.11.2020, 16:32
RE: Modbus TCP HVAC Gateway - by Daniel - 18.11.2020, 17:03
RE: Modbus TCP HVAC Gateway - by admin - 19.11.2020, 07:51
RE: Modbus TCP HVAC Gateway - by KoBra - 20.11.2020, 14:37
RE: Modbus TCP HVAC Gateway - by Daniel - 20.11.2020, 14:40
RE: Modbus TCP HVAC Gateway - by admin - 20.11.2020, 14:41
RE: Modbus TCP HVAC Gateway - by KoBra - 23.11.2020, 09:00
RE: Modbus TCP HVAC Gateway - by KoBra - 23.11.2020, 14:58
RE: Modbus TCP HVAC Gateway - by Bortolo - 25.11.2020, 05:45
RE: Modbus TCP HVAC Gateway - by admin - 25.11.2020, 07:28
RE: Modbus TCP HVAC Gateway - by KoBra - 01.12.2020, 19:07
RE: Modbus TCP HVAC Gateway - by admin - 02.12.2020, 08:29
RE: Modbus TCP HVAC Gateway - by KoBra - 02.12.2020, 09:36
RE: Modbus TCP HVAC Gateway - by Daniel - 02.12.2020, 09:40
RE: Modbus TCP HVAC Gateway - by KoBra - 02.12.2020, 09:42
RE: Modbus TCP HVAC Gateway - by Daniel - 02.12.2020, 09:45
RE: Modbus TCP HVAC Gateway - by admin - 02.12.2020, 09:45
RE: Modbus TCP HVAC Gateway - by KoBra - 02.12.2020, 10:02
RE: Modbus TCP HVAC Gateway - by admin - 02.12.2020, 10:10
RE: Modbus TCP HVAC Gateway - by KoBra - 02.12.2020, 13:08

Forum Jump: