This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

DSE7320 Modbus help
#1
Hi,

I need some help regarding a DSE7320 power generator controller.

I am having trouble to understand what should i send on modbus in order to select a workig mode (for example "Select Stop mode")
The manual states:

"The register array is divided into 256 pages each containing up to 256 registers, the actual register address is obtained from the formula:
register_address=page_number*256+register_offset."


"One of the system control keys from the table below must be written into register 8 and its ones-compliment written into register 9 with a single function 16 (write multiple registers) to perform the specified system control function."

Below are the two pages with the control functions and it's address
   

   

Any help would be much appreciated.

Thank you in advance
George
Reply


Messages In This Thread
DSE7320 Modbus help - by gtsamis - 18.12.2020, 12:51
RE: DSE7320 Modbus help - by admin - 18.12.2020, 12:59
RE: DSE7320 Modbus help - by gtsamis - 18.12.2020, 13:11
RE: DSE7320 Modbus help - by admin - 18.12.2020, 13:24
RE: DSE7320 Modbus help - by gtsamis - 21.12.2020, 08:35
RE: DSE7320 Modbus help - by gtsamis - 26.12.2020, 18:06
RE: DSE7320 Modbus help - by admin - 28.12.2020, 08:07
RE: DSE7320 Modbus help - by gtsamis - 28.12.2020, 08:16