This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Wiser for KNX and modbus problem
#14
Are you sure that you don't have even or odd parity enabled on Modbus devices? Most devices have parity and stop bits configured separately but 2 stop bits can only be enabled if parity bit is disabled.

You can log what is being received by using a script. Disable RTU in Modbus mapper before running it. Change serial port settings as needed. https://forum.logicmachine.net/showthrea...2#pid16012
Reply