11.02.2021, 09:35
Are you sure that you don't have even or odd parity enabled on Modbus devices? Most devices have parity and stop bits configured separately but 2 stop bits can only be enabled if parity bit is disabled.
You can log what is being received by using a script. Disable RTU in Modbus mapper before running it. Change serial port settings as needed. https://forum.logicmachine.net/showthrea...2#pid16012