This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Zigbee gateway integration
(13.09.2023, 12:09)admin Wrote: @Zen, we are still testing Danfoss valve but from what we've seen it's not better than others. It turns out that operating mode cannot be changed - it's permanently in heating mode, so only the setpoint can be adjusted. Some improvements will be made in the next app version.

Today, i'm testing Danfoss Ally with the newest update and it seems to fully work and communicate in bidirectional way. I can read setpoint/temperature and write the setpoint via LM5. 
Thank you.

I'll keep it active for some days to test the durability and understand if i've got the some problems i had with wiser trvs.

Update 2023-10-23: TRVs are still connected, still communicating bidirectionally and the last setpoint i've set 3 days ago is helded correctly. I can see signal/battery level too.
Reply


Messages In This Thread
Zigbee gateway integration - by tigi - 26.04.2021, 14:28
RE: Zigbee gateway integration - by myg - 26.04.2021, 15:24
RE: Zigbee gateway integration - by Daniel - 26.04.2021, 15:38
RE: Zigbee gateway integration - by tigi - 26.04.2021, 16:00
RE: Zigbee gateway integration - by Daniel - 26.04.2021, 16:04
RE: Zigbee gateway integration - by tigi - 28.04.2021, 19:35
RE: Zigbee gateway integration - by admin - 29.04.2021, 07:36
RE: Zigbee gateway integration - by tigi - 05.05.2021, 12:47
RE: Zigbee gateway integration - by Daniel - 05.05.2021, 12:48
RE: Zigbee gateway integration - by tigi - 05.05.2021, 12:55
RE: Zigbee gateway integration - by Daniel - 05.05.2021, 13:01
RE: Zigbee gateway integration - by tigi - 05.05.2021, 15:50
RE: Zigbee gateway integration - by admin - 08.05.2021, 10:16
RE: Zigbee gateway integration - by tigi - 08.05.2021, 11:09
RE: Zigbee gateway integration - by clue9 - 13.05.2021, 14:35
RE: Zigbee gateway integration - by Daniel - 13.05.2021, 14:41
RE: Zigbee gateway integration - by clue9 - 15.05.2021, 14:23
RE: Zigbee gateway integration - by MLa - 14.05.2021, 21:05
RE: Zigbee gateway integration - by clue9 - 15.05.2021, 16:25
RE: Zigbee gateway integration - by admin - 17.05.2021, 07:12
RE: Zigbee gateway integration - by emme - 19.05.2021, 16:48
RE: Zigbee gateway integration - by Daniel - 20.05.2021, 08:31
RE: Zigbee gateway integration - by admin - 21.05.2021, 13:12
RE: Zigbee gateway integration - by tigi - 21.05.2021, 16:23
RE: Zigbee gateway integration - by admin - 24.05.2021, 09:45
RE: Zigbee gateway integration - by tigi - 28.05.2021, 17:10
RE: Zigbee gateway integration - by admin - 29.05.2021, 09:05
RE: Zigbee gateway integration - by tigi - 29.05.2021, 14:29
RE: Zigbee gateway integration - by admin - 01.06.2021, 11:26
RE: Zigbee gateway integration - by tigi - 01.06.2021, 22:54
RE: Zigbee gateway integration - by admin - 02.06.2021, 05:21
RE: Zigbee gateway integration - by tigi - 02.06.2021, 21:36
RE: Zigbee gateway integration - by clue9 - 18.06.2021, 23:52
RE: Zigbee gateway integration - by admin - 21.06.2021, 06:36
RE: Zigbee gateway integration - by clue9 - 23.06.2021, 16:47
RE: Zigbee gateway integration - by admin - 24.06.2021, 09:57
RE: Zigbee gateway integration - by tigi - 07.07.2021, 10:22
RE: Zigbee gateway integration - by admin - 07.07.2021, 11:50
RE: Zigbee gateway integration - by tigi - 07.07.2021, 12:29
RE: Zigbee gateway integration - by tigi - 16.07.2021, 07:47
RE: Zigbee gateway integration - by admin - 16.07.2021, 07:59
RE: Zigbee gateway integration - by tigi - 16.07.2021, 13:51
RE: Zigbee gateway integration - by tigi - 19.07.2021, 20:18
RE: Zigbee gateway integration - by admin - 20.07.2021, 13:09
RE: Zigbee gateway integration - by tigi - 20.07.2021, 16:18
RE: Zigbee gateway integration - by daniel.r - 21.07.2021, 12:12
RE: Zigbee gateway integration - by Daniel - 21.07.2021, 12:13
RE: Zigbee gateway integration - by tuxtof - 11.08.2021, 04:36
RE: Zigbee gateway integration - by Daniel - 11.08.2021, 07:50
RE: Zigbee gateway integration - by tigi - 04.01.2022, 17:50
RE: Zigbee gateway integration - by Bitver - 15.09.2021, 12:56
RE: Zigbee gateway integration - by admin - 16.09.2021, 10:37
RE: Zigbee gateway integration - by emme - 18.09.2021, 08:10
RE: Zigbee gateway integration - by admin - 20.09.2021, 10:56
RE: Zigbee gateway integration - by Bitver - 24.09.2021, 12:36
RE: Zigbee gateway integration - by admin - 24.09.2021, 12:41
RE: Zigbee gateway integration - by edos - 24.09.2021, 15:28
RE: Zigbee gateway integration - by admin - 27.09.2021, 06:20
RE: Zigbee gateway integration - by edos - 27.09.2021, 07:48
RE: Zigbee gateway integration - by admin - 27.09.2021, 07:49
RE: Zigbee gateway integration - by edos - 27.09.2021, 08:27
RE: Zigbee gateway integration - by admin - 01.10.2021, 09:57
RE: Zigbee gateway integration - by tomnord - 07.10.2021, 18:03
RE: Zigbee gateway integration - by admin - 04.10.2021, 06:24
RE: Zigbee gateway integration - by Daniel - 05.10.2021, 10:07
RE: Zigbee gateway integration - by Evens - 26.10.2021, 18:46
RE: Zigbee gateway integration - by admin - 27.10.2021, 06:35
RE: Zigbee gateway integration - by Evens - 27.10.2021, 15:25
RE: Zigbee gateway integration - by admin - 02.11.2021, 09:50
RE: Zigbee gateway integration - by Evens - 03.11.2021, 19:34
RE: Zigbee gateway integration - by Daniel - 03.11.2021, 22:25
RE: Zigbee gateway integration - by Evens - 04.11.2021, 18:01
RE: Zigbee gateway integration - by Daniel - 04.11.2021, 18:03
RE: Zigbee gateway integration - by Evens - 04.11.2021, 19:29
RE: Zigbee gateway integration - by gtsamis - 04.11.2021, 23:28
RE: Zigbee gateway integration - by admin - 05.11.2021, 07:22
RE: Zigbee gateway integration - by gtsamis - 05.11.2021, 09:23
RE: Zigbee gateway integration - by clue9 - 19.11.2021, 22:54
RE: Zigbee gateway integration - by admin - 23.11.2021, 08:33
RE: Zigbee gateway integration - by admin - 23.11.2021, 10:31
RE: Zigbee gateway integration - by hocine - 09.12.2021, 10:47
RE: Zigbee gateway integration - by admin - 09.12.2021, 12:01
RE: Zigbee gateway integration - by domonorte - 31.12.2021, 09:11
RE: Zigbee gateway integration - by admin - 02.01.2022, 13:03
RE: Zigbee gateway integration - by merel - 02.01.2022, 16:35
RE: Zigbee gateway integration - by domonorte - 03.01.2022, 06:31
RE: Zigbee gateway integration - by admin - 03.01.2022, 06:25
RE: Zigbee gateway integration - by admin - 03.01.2022, 06:32
RE: Zigbee gateway integration - by domonorte - 03.01.2022, 06:36
RE: Zigbee gateway integration - by admin - 03.01.2022, 06:41
RE: Zigbee gateway integration - by Daniel - 05.01.2022, 08:51
RE: Zigbee gateway integration - by merel - 07.01.2022, 22:32
RE: Zigbee gateway integration - by admin - 10.01.2022, 08:01
RE: Zigbee gateway integration - by merel - 16.01.2022, 09:06
RE: Zigbee gateway integration - by admin - 17.01.2022, 09:30
RE: Zigbee gateway integration - by AlexLV - 24.01.2022, 22:42
RE: Zigbee gateway integration - by AlexLV - 08.02.2022, 11:37
RE: Zigbee gateway integration - by admin - 08.02.2022, 14:26
RE: Zigbee gateway integration - by AlexLV - 09.02.2022, 11:25
RE: Zigbee gateway integration - by admin - 11.02.2022, 13:18
RE: Zigbee gateway integration - by MLa - 11.02.2022, 21:49
RE: Zigbee gateway integration - by GIA - 12.02.2022, 21:49
RE: Zigbee gateway integration - by clue9 - 15.02.2022, 22:29
RE: Zigbee gateway integration - by admin - 16.02.2022, 12:42
RE: Zigbee gateway integration - by GIA - 17.02.2022, 17:16
RE: Zigbee gateway integration - by GIA - 16.02.2022, 13:25
RE: Zigbee gateway integration - by admin - 16.02.2022, 13:34
RE: Zigbee gateway integration - by MLa - 16.02.2022, 14:46
RE: Zigbee gateway integration - by admin - 17.02.2022, 14:12
RE: Zigbee gateway integration - by MLa - 17.02.2022, 17:05
RE: Zigbee gateway integration - by Daniel - 17.02.2022, 17:14
RE: Zigbee gateway integration - by clue9 - 18.02.2022, 15:18
RE: Zigbee gateway integration - by clue9 - 03.04.2022, 19:44
RE: Zigbee gateway integration - by clue9 - 30.11.2022, 21:53
RE: Zigbee gateway integration - by admin - 05.04.2022, 11:11
RE: Zigbee gateway integration - by Bitver - 05.04.2022, 14:10
RE: Zigbee gateway integration - by stativko - 13.04.2022, 14:21
RE: Zigbee gateway integration - by admin - 14.04.2022, 12:44
RE: Zigbee gateway integration - by stativko - 18.04.2022, 11:24
RE: Zigbee gateway integration - by tigi - 19.04.2022, 11:02
RE: Zigbee gateway integration - by admin - 20.04.2022, 08:20
RE: Zigbee gateway integration - by Zen - 15.06.2022, 14:41
RE: Zigbee gateway integration - by tigi - 16.07.2022, 09:04
RE: Zigbee gateway integration - by Rune - 22.04.2022, 21:15
RE: Zigbee gateway integration - by admin - 25.04.2022, 14:19
RE: Zigbee gateway integration - by Zen - 29.04.2022, 15:49
RE: Zigbee gateway integration - by admin - 02.05.2022, 08:33
RE: Zigbee gateway integration - by tigi - 29.06.2022, 11:11
RE: Zigbee gateway integration - by admin - 29.06.2022, 12:05
RE: Zigbee gateway integration - by tigi - 30.06.2022, 11:06
RE: Zigbee gateway integration - by tigi - 14.07.2022, 10:39
RE: Zigbee gateway integration - by admin - 07.07.2022, 08:30
RE: Zigbee gateway integration - by admin - 08.07.2022, 05:24
RE: Zigbee gateway integration - by admin - 20.07.2022, 10:38
RE: Zigbee gateway integration - by Rune - 13.09.2022, 11:55
RE: Zigbee gateway integration - by admin - 13.09.2022, 12:03
RE: Zigbee gateway integration - by Daniel - 14.09.2022, 15:21
RE: Zigbee gateway integration - by Rune - 20.09.2022, 10:36
RE: Zigbee gateway integration - by admin - 20.09.2022, 10:48
RE: Zigbee gateway integration - by Zen - 04.10.2022, 13:57
RE: Zigbee gateway integration - by emme - 05.10.2022, 16:04
RE: Zigbee gateway integration - by admin - 06.10.2022, 13:47
RE: Zigbee gateway integration - by Zen - 07.10.2022, 14:40
RE: Zigbee gateway integration - by Kolargol - 17.10.2022, 20:08
RE: Zigbee gateway integration - by admin - 18.10.2022, 05:52
RE: Zigbee gateway integration - by Rune - 23.10.2022, 15:26
RE: Zigbee gateway integration - by admin - 24.10.2022, 08:26
RE: Zigbee gateway integration - by Rune - 24.10.2022, 10:20
RE: Zigbee gateway integration - by admin - 25.10.2022, 10:12
RE: Zigbee gateway integration - by jmir - 30.10.2022, 17:14
RE: Zigbee gateway integration - by admin - 31.10.2022, 06:47
RE: Zigbee gateway integration - by admin - 03.11.2022, 07:37
RE: Zigbee gateway integration - by clue9 - 06.11.2022, 22:48
RE: Zigbee gateway integration - by Daniel - 07.11.2022, 09:24
RE: Zigbee gateway integration - by clue9 - 07.11.2022, 13:47
RE: Zigbee gateway integration - by Daniel - 07.11.2022, 15:35
RE: Zigbee gateway integration - by tigi - 17.11.2022, 18:09
RE: Zigbee gateway integration - by Daniel - 18.11.2022, 08:53
RE: Zigbee gateway integration - by admin - 14.11.2022, 06:54
RE: Zigbee gateway integration - by watamat - 15.11.2022, 20:54
RE: Zigbee gateway integration - by CarlS - 19.11.2022, 12:15
RE: Zigbee gateway integration - by admin - 21.11.2022, 08:19
RE: Zigbee gateway integration - by CarlS - 21.11.2022, 09:11
RE: Zigbee gateway integration - by tigi - 28.11.2022, 15:29
RE: Zigbee gateway integration - by admin - 29.11.2022, 07:57
RE: Zigbee gateway integration - by admin - 01.12.2022, 07:13
RE: Zigbee gateway integration - by clue9 - 03.12.2022, 19:13
RE: Zigbee gateway integration - by Daniel - 05.12.2022, 09:06
RE: Zigbee gateway integration - by admin - 05.12.2022, 13:47
RE: Zigbee gateway integration - by clue9 - 05.12.2022, 16:28
RE: Zigbee gateway integration - by Rune - 09.12.2022, 21:45
RE: Zigbee gateway integration - by admin - 12.12.2022, 07:11
RE: Zigbee gateway integration - by Rune - 13.12.2022, 21:49
RE: Zigbee gateway integration - by admin - 14.12.2022, 08:41
RE: Zigbee gateway integration - by Rune - 15.12.2022, 11:00
RE: Zigbee gateway integration - by Daniel - 15.12.2022, 11:05
RE: Zigbee gateway integration - by stativko - 18.12.2022, 16:27
RE: Zigbee gateway integration - by admin - 19.12.2022, 11:00
RE: Zigbee gateway integration - by Rune - 27.12.2022, 12:35
RE: Zigbee gateway integration - by admin - 27.12.2022, 12:39
RE: Zigbee gateway integration - by Rune - 27.12.2022, 12:51
RE: Zigbee gateway integration - by admin - 27.12.2022, 12:59
RE: Zigbee gateway integration - by Rune - 27.12.2022, 13:11
RE: Zigbee gateway integration - by admin - 27.12.2022, 13:30
RE: Zigbee gateway integration - by Rune - 27.12.2022, 13:59
RE: Zigbee gateway integration - by emme - 02.01.2023, 14:25
RE: Zigbee gateway integration - by admin - 03.01.2023, 09:41
RE: Zigbee gateway integration - by admin - 09.01.2023, 08:45
RE: Zigbee gateway integration - by Zen - 25.01.2023, 17:54
RE: Zigbee gateway integration - by CarlS - 25.01.2023, 19:49
RE: Zigbee gateway integration - by tomnord - 25.01.2023, 21:07
RE: Zigbee gateway integration - by CarlS - 26.01.2023, 05:57
RE: Zigbee gateway integration - by tomnord - 26.01.2023, 08:42
RE: Zigbee gateway integration - by admin - 26.01.2023, 10:50
RE: Zigbee gateway integration - by Zen - 26.01.2023, 12:12
RE: Zigbee gateway integration - by Zen - 02.02.2023, 10:46
RE: Zigbee gateway integration - by admin - 01.02.2023, 08:25
RE: Zigbee gateway integration - by admin - 02.02.2023, 11:00
RE: Zigbee gateway integration - by Daniel - 02.02.2023, 11:04
RE: Zigbee gateway integration - by Zen - 02.02.2023, 13:58
RE: Zigbee gateway integration - by Zen - 07.02.2023, 17:27
RE: Zigbee gateway integration - by admin - 08.02.2023, 08:46
RE: Zigbee gateway integration - by Zen - 08.02.2023, 16:59
RE: Zigbee gateway integration - by Zen - 13.02.2023, 11:43
RE: Zigbee gateway integration - by admin - 13.02.2023, 11:45
RE: Zigbee gateway integration - by Zen - 15.02.2023, 15:01
RE: Zigbee gateway integration - by Daniel - 15.02.2023, 15:13
RE: Zigbee gateway integration - by MLa - 17.02.2023, 18:38
RE: Zigbee gateway integration - by admin - 22.02.2023, 13:57
RE: Zigbee gateway integration - by jmir - 23.02.2023, 08:05
RE: Zigbee gateway integration - by admin - 23.02.2023, 08:22
RE: Zigbee gateway integration - by jmir - 23.02.2023, 09:32
RE: Zigbee gateway integration - by admin - 23.02.2023, 09:34
RE: Zigbee gateway integration - by jmir - 23.02.2023, 10:11
RE: Zigbee gateway integration - by MLa - 23.02.2023, 19:55
RE: Zigbee gateway integration - by MLa - 25.02.2023, 16:51
RE: Zigbee gateway integration - by Daniel - 27.02.2023, 08:38
RE: Zigbee gateway integration - by MLa - 28.02.2023, 14:59
RE: Zigbee gateway integration - by Daniel - 28.02.2023, 15:16
RE: Zigbee gateway integration - by MLa - 28.02.2023, 16:26
RE: Zigbee gateway integration - by MLa - 02.03.2023, 17:17
RE: Zigbee gateway integration - by tigi - 28.02.2023, 22:45
RE: Zigbee gateway integration - by tigi - 02.03.2023, 11:45
RE: Zigbee gateway integration - by admin - 02.03.2023, 11:47
RE: Zigbee gateway integration - by tigi - 02.03.2023, 18:32
RE: Zigbee gateway integration - by tigi - 05.03.2023, 18:35
RE: Zigbee gateway integration - by Daniel - 06.03.2023, 08:43
RE: Zigbee gateway integration - by admin - 06.03.2023, 08:44
RE: Zigbee gateway integration - by tigi - 06.03.2023, 18:29
RE: Zigbee gateway integration - by jeeone - 11.04.2023, 07:17
RE: Zigbee gateway integration - by admin - 11.04.2023, 07:32
RE: Zigbee gateway integration - by jeeone - 11.04.2023, 08:06
RE: Zigbee gateway integration - by jeeone - 11.04.2023, 15:02
RE: Zigbee gateway integration - by Zen - 13.04.2023, 15:27
RE: Zigbee gateway integration - by Zen - 29.06.2023, 06:52
RE: Zigbee gateway integration - by admin - 25.04.2023, 11:01
RE: Zigbee gateway integration - by CarlS - 25.04.2023, 16:42
RE: Zigbee gateway integration - by admin - 25.04.2023, 16:48
RE: Zigbee gateway integration - by CarlS - 25.04.2023, 17:50
RE: Zigbee gateway integration - by CarlS - 26.04.2023, 15:45
RE: Zigbee gateway integration - by admin - 27.04.2023, 11:01
RE: Zigbee gateway integration - by CarlS - 27.04.2023, 11:39
RE: Zigbee gateway integration - by emme - 29.04.2023, 08:00
RE: Zigbee gateway integration - by MLa - 23.05.2023, 18:09
RE: Zigbee gateway integration - by admin - 24.05.2023, 07:52
RE: Zigbee gateway integration - by MLa - 24.05.2023, 17:35
RE: Zigbee gateway integration - by ikhy - 24.05.2023, 08:20
RE: Zigbee gateway integration - by admin - 24.05.2023, 08:33
RE: Zigbee gateway integration - by ikhy - 24.05.2023, 09:01
RE: Zigbee gateway integration - by admin - 25.05.2023, 07:09
RE: Zigbee gateway integration - by MLa - 03.06.2023, 08:15
RE: Zigbee gateway integration - by Rune - 31.05.2023, 19:34
RE: Zigbee gateway integration - by AISystem - 01.06.2023, 14:42
RE: Zigbee gateway integration - by admin - 01.06.2023, 17:04
RE: Zigbee gateway integration - by AISystem - 02.06.2023, 06:07
RE: Zigbee gateway integration - by admin - 02.06.2023, 06:13
RE: Zigbee gateway integration - by AISystem - 02.06.2023, 06:52
RE: Zigbee gateway integration - by admin - 02.06.2023, 07:10
RE: Zigbee gateway integration - by AISystem - 02.06.2023, 07:24
RE: Zigbee gateway integration - by admin - 02.06.2023, 07:47
RE: Zigbee gateway integration - by admin - 05.06.2023, 06:20
RE: Zigbee gateway integration - by MLa - 05.06.2023, 19:23
RE: Zigbee gateway integration - by Daniel - 06.06.2023, 08:29
RE: Zigbee gateway integration - by ikhy - 06.06.2023, 08:15
RE: Zigbee gateway integration - by AISystem - 07.06.2023, 05:22
RE: Zigbee gateway integration - by admin - 07.06.2023, 05:23
RE: Zigbee gateway integration - by AISystem - 07.06.2023, 06:14
RE: Zigbee gateway integration - by admin - 08.06.2023, 07:34
RE: Zigbee gateway integration - by AISystem - 08.06.2023, 11:01
RE: Zigbee gateway integration - by ikhy - 08.06.2023, 18:39
RE: Zigbee gateway integration - by ikhy - 09.06.2023, 06:16
RE: Zigbee gateway integration - by Daniel - 09.06.2023, 07:38
RE: Zigbee gateway integration - by ikhy - 09.06.2023, 08:00
RE: Zigbee gateway integration - by Daniel - 09.06.2023, 08:03
RE: Zigbee gateway integration - by ikhy - 09.06.2023, 11:42
RE: Zigbee gateway integration - by ikhy - 12.06.2023, 09:09
RE: Zigbee gateway integration - by admin - 12.06.2023, 09:21
RE: Zigbee gateway integration - by Daniel - 12.06.2023, 14:34
RE: Zigbee gateway integration - by Daniel - 12.06.2023, 15:49
RE: Zigbee gateway integration - by admin - 13.06.2023, 07:34
RE: Zigbee gateway integration - by Daniel - 13.06.2023, 08:26
RE: Zigbee gateway integration - by admin - 13.06.2023, 08:30
RE: Zigbee gateway integration - by Nikita - 28.06.2023, 09:04
RE: Zigbee gateway integration - by admin - 28.06.2023, 12:20
RE: Zigbee gateway integration - by Nikita - 29.06.2023, 06:39
RE: Zigbee gateway integration - by admin - 29.06.2023, 07:07
RE: Zigbee gateway integration - by Zen - 05.07.2023, 10:04
RE: Zigbee gateway integration - by admin - 05.07.2023, 14:24
RE: Zigbee gateway integration - by Zen - 06.07.2023, 07:04
RE: Zigbee gateway integration - by Zen - 06.07.2023, 08:40
RE: Zigbee gateway integration - by cranz - 07.07.2023, 07:34
RE: Zigbee gateway integration - by Zen - 24.07.2023, 08:01
RE: Zigbee gateway integration - by Zen - 27.07.2023, 08:13
RE: Zigbee gateway integration - by Zen - 28.08.2023, 07:09
RE: Zigbee gateway integration - by Daniel - 02.08.2023, 09:53
RE: Zigbee gateway integration - by Daniel - 02.08.2023, 10:07
RE: Zigbee gateway integration - by Sral1987 - 03.08.2023, 15:33
RE: Zigbee gateway integration - by admin - 08.08.2023, 07:58
RE: Zigbee gateway integration - by jmir - 08.08.2023, 08:01
RE: Zigbee gateway integration - by Sral1987 - 09.08.2023, 12:41
RE: Zigbee gateway integration - by hocine - 14.08.2023, 14:15
RE: Zigbee gateway integration - by Daniel - 14.08.2023, 14:16
RE: Zigbee gateway integration - by hocine - 16.08.2023, 11:21
RE: Zigbee gateway integration - by admin - 28.08.2023, 07:19
RE: Zigbee gateway integration - by Zen - 30.08.2023, 07:23
RE: Zigbee gateway integration - by Sral1987 - 02.09.2023, 08:52
RE: Zigbee gateway integration - by Daniel - 04.09.2023, 07:35
RE: Zigbee gateway integration - by Sral1987 - 04.09.2023, 11:41
RE: Zigbee gateway integration - by admin - 04.09.2023, 11:45
RE: Zigbee gateway integration - by Sral1987 - 04.09.2023, 13:49
RE: Zigbee gateway integration - by MLa - 08.09.2023, 16:43
RE: Zigbee gateway integration - by admin - 11.09.2023, 09:17
RE: Zigbee gateway integration - by Zen - 12.09.2023, 14:45
RE: Zigbee gateway integration - by Sral1987 - 12.09.2023, 11:58
RE: Zigbee gateway integration - by admin - 13.09.2023, 12:09
RE: Zigbee gateway integration - by Zen - 13.09.2023, 13:58
RE: Zigbee gateway integration - by Zen - 17.10.2023, 09:19
RE: Zigbee gateway integration - by lamgia99 - 10.11.2023, 09:08
RE: Zigbee gateway integration - by admin - 13.09.2023, 14:09
RE: Zigbee gateway integration - by Zen - 14.09.2023, 09:50
RE: Zigbee gateway integration - by Sral1987 - 13.09.2023, 19:16
RE: Zigbee gateway integration - by jmir - 15.09.2023, 08:07
RE: Zigbee gateway integration - by admin - 15.09.2023, 08:39
RE: Zigbee gateway integration - by Sral1987 - 16.10.2023, 10:38
RE: Zigbee gateway integration - by Daniel - 16.10.2023, 10:39
RE: Zigbee gateway integration - by admin - 16.10.2023, 12:08
New RS-232 Zigbee gateway - by CarlS - 24.10.2023, 11:57
RE: Zigbee gateway integration - by Daniel - 24.10.2023, 12:00
RE: Zigbee gateway integration - by CarlS - 24.10.2023, 13:07
RE: Zigbee gateway integration - by admin - 24.10.2023, 13:08
RE: Zigbee gateway integration - by CarlS - 24.10.2023, 19:12
RE: Zigbee gateway integration - by admin - 02.11.2023, 10:31
RE: Zigbee gateway integration - by a455115 - 06.11.2023, 11:09
RE: Zigbee gateway integration - by admin - 06.11.2023, 11:26
RE: Zigbee gateway integration - by domotiqa - 07.11.2023, 17:03
RE: Zigbee gateway integration - by a455115 - 10.11.2023, 11:06
RE: Zigbee gateway integration - by admin - 10.11.2023, 11:18
RE: Zigbee gateway integration - by lamgia99 - 11.11.2023, 01:22
RE: Zigbee gateway integration - by domotiqa - 14.11.2023, 10:46
RE: Zigbee gateway integration - by admin - 13.11.2023, 08:12
RE: Zigbee gateway integration - by lamgia99 - 14.11.2023, 06:37
RE: Zigbee gateway integration - by lamgia99 - 16.11.2023, 01:24
RE: Zigbee gateway integration - by admin - 16.11.2023, 08:13
RE: Zigbee gateway integration - by lamgia99 - 16.11.2023, 08:26
RE: Zigbee gateway integration - by DGrandes - 17.11.2023, 14:55
RE: Zigbee gateway integration - by Daniel - 17.11.2023, 15:00
RE: Zigbee gateway integration - by DGrandes - 17.11.2023, 15:03
RE: Zigbee gateway integration - by Daniel - 17.11.2023, 15:06
RE: Zigbee gateway integration - by DGrandes - 17.11.2023, 15:23
RE: Zigbee gateway integration - by Zen - 22.11.2023, 08:38
RE: Zigbee gateway integration - by admin - 22.11.2023, 08:50
RE: Zigbee gateway integration - by Zen - 27.11.2023, 10:55
RE: Zigbee gateway integration - by tom77 - 28.11.2023, 10:53
RE: Zigbee gateway integration - by admin - 28.11.2023, 11:15
RE: Zigbee gateway integration - by Zen - 28.11.2023, 15:08
RE: Zigbee gateway integration - by domotiqa - 29.11.2023, 09:13
RE: Zigbee gateway integration - by admin - 29.11.2023, 12:03
RE: Zigbee gateway integration - by tigi - 08.12.2023, 10:24
RE: Zigbee gateway integration - by Daniel - 08.12.2023, 10:29
RE: Zigbee gateway integration - by tigi - 08.12.2023, 10:34
RE: Zigbee gateway integration - by tigi - 10.12.2023, 19:27
RE: Zigbee gateway integration - by tigi - 13.12.2023, 13:52
RE: Zigbee gateway integration - by admin - 13.12.2023, 13:52
RE: Zigbee gateway integration - by tigi - 13.12.2023, 14:13
RE: Zigbee gateway integration - by tomnord - 14.12.2023, 14:15
RE: Zigbee gateway integration - by admin - 14.12.2023, 14:52
RE: Zigbee gateway integration - by tomnord - 15.12.2023, 07:18
RE: Zigbee gateway integration - by admin - 15.12.2023, 08:11
RE: Zigbee gateway integration - by tomnord - 15.12.2023, 13:27
RE: Zigbee gateway integration - by admin - 15.12.2023, 13:30
RE: Zigbee gateway integration - by tomnord - 31.12.2023, 10:32
RE: Zigbee gateway integration - by admin - 02.01.2024, 10:17
RE: Zigbee gateway integration - by tomnord - 02.01.2024, 12:28
RE: Zigbee gateway integration - by admin - 02.01.2024, 12:31
RE: Zigbee gateway integration - by tomnord - 02.01.2024, 16:11
RE: Zigbee gateway integration - by Daniel - 02.01.2024, 16:30
RE: Zigbee gateway integration - by Sral1987 - 03.01.2024, 12:57
RE: Zigbee gateway integration - by admin - 03.01.2024, 14:04
RE: Zigbee gateway integration - by alexll - 03.01.2024, 16:40
RE: Zigbee gateway integration - by Sral1987 - 06.01.2024, 14:30
RE: Zigbee gateway integration - by tomnord - 18.01.2024, 20:33
RE: Zigbee gateway integration - by Daniel - 19.01.2024, 08:30
RE: Zigbee gateway integration - by tomnord - 19.01.2024, 09:35
RE: Zigbee gateway integration - by admin - 19.01.2024, 09:42
RE: Zigbee gateway integration - by tomnord - 19.01.2024, 09:57
RE: Zigbee gateway integration - by admin - 19.01.2024, 10:05
RE: Zigbee gateway integration - by tomnord - 19.01.2024, 10:49
RE: Zigbee gateway integration - by tomnord - 20.01.2024, 09:53
RE: Zigbee gateway integration - by tomnord - 25.01.2024, 18:17
RE: Zigbee gateway integration - by Daniel - 26.01.2024, 08:28
RE: Zigbee gateway integration - by tomnord - 26.01.2024, 08:38
RE: Zigbee gateway integration - by Daniel - 26.01.2024, 08:40
RE: Zigbee gateway integration - by Zen - 29.01.2024, 15:10
RE: Zigbee gateway integration - by admin - 01.02.2024, 14:12
RE: Zigbee gateway integration - by admin - 13.02.2024, 08:03
RE: Zigbee gateway integration - by AlexandrT - 13.02.2024, 16:34
RE: Zigbee gateway integration - by Patrik - 13.02.2024, 20:50
RE: Zigbee gateway integration - by admin - 14.02.2024, 10:44
RE: Zigbee gateway integration - by AlexandrT - 14.02.2024, 15:00
RE: Zigbee gateway integration - by Rune - 16.02.2024, 12:03
RE: Zigbee gateway integration - by admin - 19.02.2024, 08:33
RE: Zigbee gateway integration - by AlexLV - 25.02.2024, 23:02
RE: Zigbee gateway integration - by Daniel - 26.02.2024, 08:55
RE: Zigbee gateway integration - by AlexLV - 26.02.2024, 15:17
RE: Zigbee gateway integration - by admin - 04.03.2024, 08:33
RE: Zigbee gateway integration - by admin - 04.03.2024, 09:25
RE: Zigbee gateway integration - by admin - 04.03.2024, 10:44
RE: Zigbee gateway integration - by busta - 29.03.2024, 12:57
RE: Zigbee gateway integration - by admin - 02.04.2024, 07:16
RE: Zigbee gateway integration - by alexll - 24.04.2024, 13:48
RE: Zigbee gateway integration - by busta - 25.04.2024, 17:17
RE: Zigbee gateway integration - by admin - 26.04.2024, 09:59
Zigbee gateway - by CristianAgata - 06.03.2022, 13:38
RE: Zigbee gateway - by admin - 07.03.2022, 07:40
RE: Zigbee gateway - by CristianAgata - 07.03.2022, 12:00
RE: Zigbee gateway - by admin - 07.03.2022, 12:07
RE: Zigbee gateway - by CristianAgata - 07.03.2022, 12:10
RE: Zigbee gateway - by CristianAgata - 13.03.2022, 11:37
RE: Zigbee gateway - by admin - 14.03.2022, 10:25
RE: Zigbee gateway - by CristianAgata - 14.03.2022, 11:06
RE: Zigbee gateway - by admin - 21.03.2022, 13:38
RE: Zigbee gateway - by emme - 02.04.2022, 08:48
RE: Zigbee gateway - by CristianAgata - 02.04.2022, 16:02
RE: Zigbee gateway - by clue9 - 03.04.2022, 19:11
RE: Zigbee gateway - by admin - 05.04.2022, 11:19
RE: Zigbee gateway - by gilles38 - 07.06.2022, 13:43
RE: Zigbee gateway - by admin - 10.06.2022, 09:45
RE: Zigbee gateway - by gilles38 - 13.06.2022, 10:59
RE: Zigbee gateway - by CarlS - 30.09.2022, 05:34
RE: Zigbee gateway - by CarlS - 18.10.2022, 06:24
RE: Zigbee gateway - by admin - 18.10.2022, 10:29
RE: Zigbee gateway - by watamat - 19.10.2022, 19:42
RE: Zigbee gateway - by admin - 20.10.2022, 06:20
RE: Zigbee gateway - by simone.muscat - 20.10.2022, 06:31
RE: Zigbee gateway - by watamat - 20.10.2022, 19:31
RE: Zigbee gateway - by watamat - 01.11.2022, 14:08
RE: Zigbee gateway - by watamat - 12.11.2022, 16:27

Forum Jump: