This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

BAcnet BBMD
#5
You must see a BBMD as a tunnel between 2 BACnet networks, it takes a broadcast message from network 1 as unicast message and broadcast it on the secondary network again. Only ONE BBMD should be configured per TCP/IP subnet. I repeat ONLY ONE !  Just like KNX routers you can only have one tunnel between your 2 networks to avoid loops.

As you can see in this image you need a BBMD in each network, if you only have one BBMD you might want to register it as foreign device..
   
   