This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

I can't write on Modbus
#7
Thanks for the access. Writing for CALEFFI GW PRO is working fine, I've tested by changing the setpoint. For ALDES INSPIRAIR you need to modify the profile and add these fields for all entries with writable set to true: