This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus RTU and TCP
#1
Hi,

On a project we have two modbus devices connected to a LM3 Lite (latest firmware), the first one is RTU port 1 and the second one is TCP.

RTU device only allows read/write one register each second, so in the profile has the field "read_delay"=1 (and it works fine). We're reading about 60 registers from this the device.
It seems that, depending on the value of "Poll Interval", the second device (TCP) is not read..
If we set the poll interval to 120s on the RTU device, then TCP is read.

Has something been changed on last firmwares? On older ones we have not seen this behavior...
How are modbus readings/writings processed? Sequentially slave to slave despite if they are on the same port or not?

We've seen that writings to RTU device are done passed some time after they are done on KNX side (sometimes after 1 minute....). How are they done after the actual polling, on the next one?
Reply


Messages In This Thread
Modbus RTU and TCP - by jmir - 06.05.2022, 06:30
RE: Modbus RTU and TCP - by admin - 06.05.2022, 08:22
RE: Modbus RTU and TCP - by jmir - 06.05.2022, 08:33
RE: Modbus RTU and TCP - by admin - 06.05.2022, 08:44
RE: Modbus RTU and TCP - by jmir - 06.05.2022, 08:57
RE: Modbus RTU and TCP - by admin - 06.05.2022, 11:05
RE: Modbus RTU and TCP - by jmir - 10.05.2022, 07:00
RE: Modbus RTU and TCP - by jmir - 16.05.2022, 05:53
RE: Modbus RTU and TCP - by Daniel - 16.05.2022, 07:38
RE: Modbus RTU and TCP - by admin - 16.05.2022, 07:41
RE: Modbus RTU and TCP - by jmir - 17.05.2022, 09:54