This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Big problem with Modbus TCP
#6
Are you sure that values don't overflow because object data type is smaller? For UINT8 any value larger than 255 will be written as 255.