01.03.2017, 23:12
(This post was last modified: 01.03.2017, 23:24 by Erwin van der Zwart.)
Hi,
I see you have a lot of trends and small resolution (5 min?), what is the total size of all your trends?
It can be that if it's more then 40-50 MB in total of trends you encounter this issue on HL/SL/LM.
If this is the case i would advice to reduce the lenght of your trends and/or change resolution to lower resolution due to system resources.
In new FW there will be a limit set to avoid making to much trend load that can result to this kind of behavior.
BR,
Erwin
I see you have a lot of trends and small resolution (5 min?), what is the total size of all your trends?
It can be that if it's more then 40-50 MB in total of trends you encounter this issue on HL/SL/LM.
If this is the case i would advice to reduce the lenght of your trends and/or change resolution to lower resolution due to system resources.
In new FW there will be a limit set to avoid making to much trend load that can result to this kind of behavior.
BR,
Erwin