Threads: 5
When exporting points to BACnet - How many points can be exported on the different devices?
Schneider has informed that:
- Wiser for KNX / homeLYnk = 500 point limit
- SpaceLYnk = 800 point limit
How many points can the different LM's export? Is there a point cap here?
-CDG
Threads: 46
LM does not have any limits though we do not recommend having more than 2000 objects
Threads: 7
23.01.2019, 20:12
(This post was last modified: 23.01.2019, 23:04 by Erwin van der Zwart.)
Wiser for KNX has a software limit to 150 points, spaceLYnk is just like LM without restrictions.
We run tests in our lab to determine the recommended number of BACnet objects and we just finalized the HW3 tests. Here are the results:
There is recommended limit for 500 objects exportable to BACnet for HW1 in the user guide which can be reviewed based on this test report. The HW3 can handle up to 2000 object with respect to other running processes, activities and assuming that there is not traffic on KNX bus. When KNX traffic is present the limits must be modified accordingly.
Threads: 5
Thanks for the input on the matter.