Norwegian HAN-interface - Kamstrup meter
Hello
I am planing to make a script that receives the power data from a Kamstrup Power meter.
In Norway all the power meters has been changed to smart meters, and one of the requirement from the government, was that customer should have access to the data.
Google translate this site for more info:
https://www.nek.no/info-ams-han-utviklere/
As far as i know there is 3 types of power meters used, Kamstrup, Aidon and Kaifa.
They are all sending (pushing) data on a port (Physical interface is MBUS), and the data can be read with a Mbus to serial converter (slave type). I am using this, to connect LM to my Kamstrup meter:
https://www.aliexpress.com/item/USB-tran...62958.html
Since i have a Kamstrup meter, i will focus on that type in this thread.
More info about Kamstrup HAN interface
https://www.nek.no/wp-content/uploads/20...181022.pdf
https://www.nek.no/wp-content/uploads/20...ev_3_1.pdf
-- Check if port is open, open serial port if not if not port then  require('serial')  port = serial.open('/dev/ttyUSB0', { baudrate = 2400 })  port:flush()  data = '' end -- Read on byte, or time out after 1 sec byte = port:read(1, 1) if byte then  -- if byte read, add byte to data array  data = data .. byte else  -- read timeout: No more data in this package  if string.len(data) > 1 then    loghex(data)  end  data = "" end
Here is a residential script that reads the data, pushed from the kamstrup meter.
There is two types of packages:
- every 10 sec we get the basic data
- every 1 hr we get the basic + a little bit more.
Example of a basic data (ID replaced with XX):
* hexstring [228]: 7E A0 E2 2B 21 13 23 9A E6 E7 00 0F 00 00 00 00 0C 07 E3 01 1F 04 0D 24 0A FF 80 00 00 02 19 0A 0E 4B 61 6D 73 74 72 75 70 5F 56 30 30 30 31 09 06 01 01 00 00 05 FF 0A 10 XX XX XX XX XX XX XX XX XX XX XX XX XX XX XX XX 09 06 01 01 60 01 01 FF 0A 12 36 38 34 31 31 32 31 42 4E 32 34 33 31 30 31 30 34 30 09 06 01 01 01 07 00 FF 06 00 00 0E BB 09 06 01 01 02 07 00 FF 06 00 00 00 00 09 06 01 01 03 07 00 FF 06 00 00 01 C4 09 06 01 01 04 07 00 FF 06 00 00 00 00 09 06 01 01 1F 07 00 FF 06 00 00 05 C1 09 06 01 01 33 07 00 FF 06 00 00 03 27 09 06 01 01 47 07 00 FF 06 00 00 03 91 09 06 01 01 20 07 00 FF 12 00 DC 09 06 01 01 34 07 00 FF 12 00 DE 09 06 01 01 48 07 00 FF 12 00 DD F7 9B 7E
Start flag      7E                A0 E2 2B 21 13 23 9A E6 E7 00 Date/time       0F 00 00 00 00      0C 07 E3 01 1F 04 0D 24 0A FF 80 00 00                02 19                0E 4B   Kamstrup_V0001  61 6D 73 74 72 75 70 5F 56 30 30 30 31 ID              09 06 01 01 00 00 05 FF    0A 10 XX XX XX XX XX XX XX XX XX XX XX XX XX XX XX XX Type            09 06 01 01 60 01 01 FF    0A 12 36 38 34 31 31 32 31 42 4E 32 34 33 31 30 31 30 34 30 (6841121BN243101040) Act Pow+        09 06 01 01 01 07 00 FF    06 00 00 0E BB Act Pow-        09 06 01 01 02 07 00 FF    06 00 00 00 00 Rea Pow+        09 06 01 01 03 07 00 FF    06 00 00 01 C4 Rea Pow-        09 06 01 01 04 07 00 FF    06 00 00 00 00 Current         09 06 01 01 1F 07 00 FF    06 00 00 05 C1 Current         09 06 01 01 33 07 00 FF    06 00 00 03 27 Current         09 06 01 01 47 07 00 FF    06 00 00 03 91 Voltage         09 06 01 01 20 07 00 FF    12 00 DC Voltage         09 06 01 01 34 07 00 FF    12 00 DE Voltage         09 06 01 01 48 07 00 FF    12 00 DD CRC             F7 9B Stop flag       7E
CRC
The checksum is the same as the CRC-16/X-25 on this site: https://crccalc.com/
Remove start and end byte (7E) + CRC bytes.
Both of the following functions should work:
function crc16(data)  local crc = 0xFFFF for i = 1, #data do    crc = bit.bxor(crc, data:byte(i))    for j = 1, 8 do      local k = bit.band(crc, 1)      crc = bit.rshift(crc, 1)      if k ~= 0 then        crc = bit.bxor(crc, 0x8408)        end      end    end    --return bit.bxor(crc, 0xFFFF)    return string.format("%X",bit.bxor(crc, 0xFFFF)) end
local crcTable = {        0x0000, 0x1189, 0x2312, 0x329b, 0x4624, 0x57ad, 0x6536, 0x74bf,        0x8c48, 0x9dc1, 0xaf5a, 0xbed3, 0xca6c, 0xdbe5, 0xe97e, 0xf8f7,        0x1081, 0x0108, 0x3393, 0x221a, 0x56a5, 0x472c, 0x75b7, 0x643e,        0x9cc9, 0x8d40, 0xbfdb, 0xae52, 0xdaed, 0xcb64, 0xf9ff, 0xe876,        0x2102, 0x308b, 0x0210, 0x1399, 0x6726, 0x76af, 0x4434, 0x55bd,        0xad4a, 0xbcc3, 0x8e58, 0x9fd1, 0xeb6e, 0xfae7, 0xc87c, 0xd9f5,        0x3183, 0x200a, 0x1291, 0x0318, 0x77a7, 0x662e, 0x54b5, 0x453c,        0xbdcb, 0xac42, 0x9ed9, 0x8f50, 0xfbef, 0xea66, 0xd8fd, 0xc974,        0x4204, 0x538d, 0x6116, 0x709f, 0x0420, 0x15a9, 0x2732, 0x36bb,        0xce4c, 0xdfc5, 0xed5e, 0xfcd7, 0x8868, 0x99e1, 0xab7a, 0xbaf3,        0x5285, 0x430c, 0x7197, 0x601e, 0x14a1, 0x0528, 0x37b3, 0x263a,        0xdecd, 0xcf44, 0xfddf, 0xec56, 0x98e9, 0x8960, 0xbbfb, 0xaa72,        0x6306, 0x728f, 0x4014, 0x519d, 0x2522, 0x34ab, 0x0630, 0x17b9,        0xef4e, 0xfec7, 0xcc5c, 0xddd5, 0xa96a, 0xb8e3, 0x8a78, 0x9bf1,        0x7387, 0x620e, 0x5095, 0x411c, 0x35a3, 0x242a, 0x16b1, 0x0738,        0xffcf, 0xee46, 0xdcdd, 0xcd54, 0xb9eb, 0xa862, 0x9af9, 0x8b70,        0x8408, 0x9581, 0xa71a, 0xb693, 0xc22c, 0xd3a5, 0xe13e, 0xf0b7,        0x0840, 0x19c9, 0x2b52, 0x3adb, 0x4e64, 0x5fed, 0x6d76, 0x7cff,        0x9489, 0x8500, 0xb79b, 0xa612, 0xd2ad, 0xc324, 0xf1bf, 0xe036,        0x18c1, 0x0948, 0x3bd3, 0x2a5a, 0x5ee5, 0x4f6c, 0x7df7, 0x6c7e,        0xa50a, 0xb483, 0x8618, 0x9791, 0xe32e, 0xf2a7, 0xc03c, 0xd1b5,        0x2942, 0x38cb, 0x0a50, 0x1bd9, 0x6f66, 0x7eef, 0x4c74, 0x5dfd,        0xb58b, 0xa402, 0x9699, 0x8710, 0xf3af, 0xe226, 0xd0bd, 0xc134,        0x39c3, 0x284a, 0x1ad1, 0x0b58, 0x7fe7, 0x6e6e, 0x5cf5, 0x4d7c,        0xc60c, 0xd785, 0xe51e, 0xf497, 0x8028, 0x91a1, 0xa33a, 0xb2b3,        0x4a44, 0x5bcd, 0x6956, 0x78df, 0x0c60, 0x1de9, 0x2f72, 0x3efb,        0xd68d, 0xc704, 0xf59f, 0xe416, 0x90a9, 0x8120, 0xb3bb, 0xa232,        0x5ac5, 0x4b4c, 0x79d7, 0x685e, 0x1ce1, 0x0d68, 0x3ff3, 0x2e7a,        0xe70e, 0xf687, 0xc41c, 0xd595, 0xa12a, 0xb0a3, 0x8238, 0x93b1,        0x6b46, 0x7acf, 0x4854, 0x59dd, 0x2d62, 0x3ceb, 0x0e70, 0x1ff9,        0xf78f, 0xe606, 0xd49d, 0xc514, 0xb1ab, 0xa022, 0x92b9, 0x8330,        0x7bc7, 0x6a4e, 0x58d5, 0x495c, 0x3de3, 0x2c6a, 0x1ef1, 0x0f78 } function crc16(v)     local crc = 0xffff          for i = 1, #v do             local j = bit.band( bit.bxor( v:byte(i), crc ),  0xFF )             crc = bit.band( bit.bxor(crcTable[j+1], bit.rshift(crc, 8)), 0xffff)     end          return bit.bxor(crc, 0xffff) end
I am new to LUA, so please help optimize the code  Smile
Will update this post when i have more info..
Basic receive logic:
Receive 1 byte with 1 second timeout
  • In case of timeout, check if buffer is not empty and parse it
  • Otherwise add byte to buffer
The third byte seems to be packet length without first/last 0x7E so you can use that to parse buffer with multiple messages in case they arrive together (10 second and 1 hour data).
(31.01.2019, 13:58)admin Wrote: Basic receive logic:
Can you please provide an example?
(31.01.2019, 13:58)admin Wrote: The third byte seems to be packet length without first/last 0x7E so you can use that to parse buffer with multiple messages in case they arrive together (10 second and 1 hour data).
Yes, actually it is both 3rd and lower part on 2nd, but the 1 hr and 10 sec message should not come together:
Quote:Push interval: Fixed at 3600s, The 10 second timer and the 1 hour timer must not collide since then one of the lists will not be pushed. So the 10 sec timer will be sent at xx:xx:x0 (hh:mmConfuseds) and the 1 hour timer is offset 5 seconds and sent at xx:00:05 (hh:mmConfuseds)
Some more sample data. ID-bytes have been replaced with 0x01, and checksum bytes have been updated accordingly
# 3 examples of 10 sec message. ID changed to 1111... and CRC updated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examples of 1 hr message. ID changed to 1111... and CRC updated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
Your example already does what I've suggested. The only slight improvement is to use a table to buffer data.
-- Check if port is open, open serial port if not if not port then   require('serial')   port = serial.open('/dev/ttyUSB0', { baudrate = 2400 })   port:flush()   buffer = {} end -- Read on byte, or time out after 1 sec char = port:read(1, 1) if char then   buffer[ #buffer + 1 ] = char elseif #buffer > 0 then   data = table.concat(buffer)   -- parse(data)   loghex(data)   buffer = {} end
Hi , was just wondering did you get this working?
Thanks for improvement suggestion, Admin. I didn't know that successive concatenations to a single string have poor performance. Smile I am new to LUA, so i appreciate feedback, how to optimize the code.
Tokatubs.
Working away from home at the moment, and will not be able to test before end of February.
However, i did bring some samples of the data packages sent from the meter with me, and have been playing a little bit with them on my Laptop.
My first plan was to iterate through the whole package, and parse all the obis data and values. But since the packages always have the data i need in the same position every time, i decided that verifying the data package, and read out the data from the known position, would be both easier for me and less demanding for the LM.
Here is the code i have so far, works fine in ZeroBrane Studio:
------------------------------------------------------------------------------------ -- Sample data from 3 phase Kamstrup power meter -- Type: 6841121BN243101040 -- Tested on ZeroBrane Studio, with Lua Interpreter: Lua (LuaJit) ------------------------------------------------------------------------------------ -- LuaJIT BitOp, same as LM bit lib? local bit = require("bit") -- 10 sec sample telegrams sample_1 = string.char( 0x7e, 0xa0, 0xe2, 0x2b, 0x21, 0x13, 0x23, 0x9a, 0xe6, 0xe7, 0x00, 0x0f, 0x00, 0x00, 0x00, 0x00, 0x0c, 0x07, 0xe3, 0x01, 0x15, 0x01, 0x17, 0x2b, 0x0a, 0xff, 0x80, 0x00, 0x00, 0x02, 0x19, 0x0a, 0x0e, 0x4b, 0x61, 0x6d, 0x73, 0x74, 0x72, 0x75, 0x70, 0x5f, 0x56, 0x30, 0x30, 0x30, 0x31, 0x09, 0x06, 0x01, 0x01, 0x00, 0x00, 0x05, 0xff, 0x0a, 0x10, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x09, 0x06, 0x01, 0x01, 0x60, 0x01, 0x01, 0xff, 0x0a, 0x12, 0x36, 0x38, 0x34, 0x31, 0x31, 0x32, 0x31, 0x42, 0x4e, 0x32, 0x34, 0x33, 0x31, 0x30, 0x31, 0x30, 0x34, 0x30, 0x09, 0x06, 0x01, 0x01, 0x01, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x0b, 0x08, 0x09, 0x06, 0x01, 0x01, 0x02, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x00, 0x00, 0x09, 0x06, 0x01, 0x01, 0x03, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x01, 0xd1, 0x09, 0x06, 0x01, 0x01, 0x04, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x00, 0x00, 0x09, 0x06, 0x01, 0x01, 0x1f, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x04, 0x43, 0x09, 0x06, 0x01, 0x01, 0x33, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x02, 0xee, 0x09, 0x06, 0x01, 0x01, 0x47, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x02, 0x2d, 0x09, 0x06, 0x01, 0x01, 0x20, 0x07, 0x00, 0xff, 0x12, 0x00, 0xdc, 0x09, 0x06, 0x01, 0x01, 0x34, 0x07, 0x00, 0xff, 0x12, 0x00, 0xdd, 0x09, 0x06, 0x01, 0x01, 0x48, 0x07, 0x00, 0xff, 0x12, 0x00, 0xdf, 0x6b, 0xaa, 0x7e ) sample_2 = string.char( 0x7e, 0xa0, 0xe2, 0x2b, 0x21, 0x13, 0x23, 0x9a, 0xe6, 0xe7, 0x00, 0x0f, 0x00, 0x00, 0x00, 0x00, 0x0c, 0x07, 0xe3, 0x01, 0x1d, 0x02, 0x09, 0x39, 0x1e, 0xff, 0x80, 0x00, 0x00, 0x02, 0x19, 0x0a, 0x0e, 0x4b, 0x61, 0x6d, 0x73, 0x74, 0x72, 0x75, 0x70, 0x5f, 0x56, 0x30, 0x30, 0x30, 0x31, 0x09, 0x06, 0x01, 0x01, 0x00, 0x00, 0x05, 0xff, 0x0a, 0x10, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x31, 0x09, 0x06, 0x01, 0x01, 0x60, 0x01, 0x01, 0xff, 0x0a, 0x12, 0x36, 0x38, 0x34, 0x31, 0x31, 0x32, 0x31, 0x42, 0x4e, 0x32, 0x34, 0x33, 0x31, 0x30, 0x31, 0x30, 0x34, 0x30, 0x09, 0x06, 0x01, 0x01, 0x01, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x15, 0x30, 0x09, 0x06, 0x01, 0x01, 0x02, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x00, 0x00, 0x09, 0x06, 0x01, 0x01, 0x03, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x01, 0x38, 0x09, 0x06, 0x01, 0x01, 0x04, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x00, 0x00, 0x09, 0x06, 0x01, 0x01, 0x1f, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x08, 0xab, 0x09, 0x06, 0x01, 0x01, 0x33, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x07, 0xb2, 0x09, 0x06, 0x01, 0x01, 0x47, 0x07, 0x00, 0xff, 0x06, 0x00, 0x00, 0x02, 0x37, 0x09, 0x06, 0x01, 0x01, 0x20, 0x07, 0x00, 0xff, 0x12, 0x00, 0xd6, 0x09, 0x06, 0x01, 0x01, 0x34, 0x07, 0x00, 0xff, 0x12, 0x00, 0xda, 0x09, 0x06, 0x01, 0x01, 0x48, 0x07, 0x00, 0xff, 0x12, 0x00, 0xdd, 0x21, 0x57, 0x7e ) -- Table dump / pretty print function found online: -- http://lua-users.org/wiki/TableSerialization function print_r (t, indent) -- alt version, abuse to http://richard.warburton.it  local indent=indent or ''  for key,value in pairs(t) do    io.write(indent,'[',tostring(key),']')    if type(value)=="table" then io.write(':\n') print_r(value,indent..'\t')    else io.write(' = ',tostring(value),'\n') end  end end --  Return CRC-16/X-25 function crc16(data)  local crc = 0xFFFF for i = 1, #data do    crc = bit.bxor(crc, data:byte(i))    for j = 1, 8 do      local k = bit.band(crc, 1)      crc = bit.rshift(crc, 1)      if k ~= 0 then        crc = bit.bxor(crc, 0x8408)        end      end    end    return bit.bxor(crc, 0xFFFF) end -- Convert 2 bytes to number function uint16(b)  if( #b ~= 2) then    return  else    return bit.lshift(b:byte(1),8) + b:byte(2)  end end -- Convert 4 bytes to number  function uint32(b)    if( #b ~= 4) then      return    else    --Workaround needed...  lshift(XX,24) gives som strange results on numbers bigger than 0x7f....    --return bit.lshift(b:byte(1),24) + bit.lshift(b:byte(2),16) + bit.lshift(b:byte(3),8) + b:byte(4)      return b:byte(1) * 2 ^ 24       + bit.lshift(b:byte(2),16) + bit.lshift(b:byte(3),8) + b:byte(4)    end  end   -- Convert 12 byte octet-string to date/time function date_time(b)  if (#b ~= 12) then    return  end  local weekdays = {"Mon","Tue","Wed","Thu","Fri","Sat","Sun"}  local t = {}  t.year = uint16(b:sub(1,2))  t.month = b:byte(3)  t.day = b:byte(4)  t.wday = weekdays[b:byte(5)]  t.hour = b:byte(6)  t.min = b:byte(7)  t.sec = b:byte(8)  return  t end function parse(b)     -- Check package length  if (#b ~= 228) then    print("Error: Wrong package length, 10 sec package should be 228 bytes")    return  end -- Check start and stop flag  if ( b:byte(1) ~= 0x7E or b:byte(-1) ~= 0x7E) then    print("Error: Wrong start and/or stop flag, both must be 0x7E on valid package")    return  end    -- Parse checksum bytes -> 0xAA, 0xBB -> 0xBBAA  check_sum= bit.lshift(b:byte(-2),8) + b:byte(-3)    -- Compare checksum bytes with calculated cheksum  if ( check_sum ~= crc16( b:sub(2,-4))) then    print("Error: CRC mismatch")    return  end    -- Verify list version  if ( b:sub(34,47) ~= "Kamstrup_V0001") then    print("Error: Not Kamstrup_V0001 list")    return  end    -- All looks good so far. Read out data from package  local t = {}  t.time    = date_time(b:sub(18,29))  t.version = "Kamstrup_V0001"  t.id      = b:sub(58,73)  t.type    = b:sub(84,101)  -- P: Active power in Watt  -- Q: Reactive power in kVar  -- I: Current in Amp  -- U: Voltage in Volt  t.P       = { imp = uint32(b:sub(111,114)), exp = uint32(b:sub(124,127)) }  t.Q       = { imp = uint32(b:sub(137,140)), exp = uint32(b:sub(150,153)) }  t.I       = { uint32(b:sub(163,166)) / 100, uint32(b:sub(176,179)) / 100, uint32(b:sub(189,192)) / 100 }  t.U       = { uint16(b:sub(202,203))      , uint16(b:sub(213,214))      , uint16(b:sub(224,225)) }    return t end result = parse(sample_1) --result = parse(sample_2) if (result) then    print_r(result)    --update_influxDB(result)  --update_kamstrup_grp(result)   end
Some more info how to parse the data:
Datatypes: structure        02 LL            (LL elements) octet-string     09 LL   XX ..       (LL bytes) visible-string   0A LL   XX ..       (LL bytes) unsigned32       06      XX XX XX XX    (04 bytes) unsigned16       12      XX XX        (02 bytes) OBIS CODE - octet-string[06] 09 06    01 01 1F 07 00 FF  =  1.1.31.07.00.255 Date/time - octet-string[0C] 09 0C    07 E3 01 1D 02 0B 00 05 FF 80 00 00           2019/01/29 Tu 11:00:05 Byte[1-2]    Year Byte[3]      Month Byte[4]      Day of month Byte[5]      Day of week, 1= Mon, 7 = Sun Byte[6]      Hours Byte[7]      Min Byte[8]      Sec Byte[9-0C]   .... This date/time format is also used in the header, but without the octet-string identifier 0x09
Looks good. The issue with uint32 function using bit shifts is caused by bit lib operating on signed 32-bit integers, so your solution with multiplication is correct.