Modbus variables: import massive
Dear all,
I am workin on a project on which LM will be communicate with 4 modbus devices in TCP/IP.
Every devices will have about 300 modbus variables.
Obviously I will import variables with Json file. Considering the big amount of variables is there the opportunity to link the modbus variable to KNX address in automatic and not manually step by step?
Because if I do a mistake with json file then I have to link modbus variables to knx group address again.
Is there any help about that?
You can use this script to map your modbus profiles to objects automatically.
.lua   Auto create objects and map to modbus profile.lua (Size: 1.13 KB / Downloads: 138)
PS: Make backup before you run it because there is a lot created (:
It creates 255 objects each run and skips already mapped objects, so you need to change to address scope and run it again for the next 255 objects. So for 1200 objects you need to run it 5 times.
Thank you very much Erwin,
I have seen that entries modbus are the folling:
"id", "internal_id", "device", "name", "active", "bus_write", "bus_address", "bus_datatype", "internal", "type", "value_delta","value_base","value_multiplier","value_bitmask","value_nan","value_conv","value_custom","units","address","address_scale","read_count","read_offset","read_swap","datatype","writable","write_only","write_multiple"
In json file has to be declared all of them or it is not necessary?
Mandatory fields are marked with "Required":
http://openrb.com/docs/modbus.htm
Ok then. Thanks.
I love LM because there's a solution for everything.
Thanks to all team.
how many modbus variable can used in a Spacelynk modbus profile? The device connetted will be one.
Best regards
(21.03.2019, 07:26)fabiorusco Wrote: Hello,
Best regards
Technically there is no limit but more you add you will need longer pooling time.
Best regards
I have about 500 modbus variables.
Best regards
Above they mention 4 slaves with each 300 objects so 1200 in total.
Best regards
Thank you!
I use spacelynk like a modbus slave (The master is a Scada). I will comunicate DI, AI, DO, AO with the Scada.
It's possible use modbus json profile to implement it?
Otherwise can I create a list with all the objects (modbus-KNX) and a script to implement it?
Thank you in advance.
(02.04.2019, 06:20)fabiorusco Wrote: Hello,
For slave you have to use script. Fallow this example.
http://openrb.com/lm-as-modbus-tcp-slave/
I must manage the objects of the attached pdf file.
Write a script it's no easy, without a profile.
(02.04.2019, 10:46)fabiorusco Wrote: I must manage the objects of the attached pdf file.
.pdf   ModBus Rs 485 Memory map proposal 11 0 - Lighting Node.pdf (Size: 100.84 KB / Downloads: 40)
Profiles are only for master, there is no other way. This script is very ease, you just have to fill the array for object mapping and corresponding dpts in second array.
Can you give me an example?
Thank you
I sent you already full example above.  You need to fill these arrays
 -- list of coil mapping, starting from 0  coils = { '1/1/1', '1/1/2' }  -- list of register mapping, starting from 0  registers = { '2/2/2', '3/3/3' }  -- list of register data types, element count must match registers table  regdt = { dt.int8, dt.uint16 }
Coils are binary objects and there you just add group addresses.
Registers are numeric objects and there you also have to add group addresses.
For registers you also have to add register dpt in regdt table.  In this example group 2/2/2 is dt.int8, and group 3/3/3 is dt.uint16.  For each register you need to add dpt in next table in the same order.
Hope this is clear.
The memory map that you have uses registers as bit masks. If this can be changed I suggest using coils instead which are meant for storing Boolean variables. This will make mapping to objects much easier.
The memory map is mandatory, I can't change it. How can manage the masks?
You will need extra scripts to create bitmask values from binary objects, see this post: https://forum.logicmachine.net/showthread.php?tid=1777
Here is modified slave script.  I doubled the arrays for registers and added a shift.  Fill accordingly all the arrays.  registers1 will start from 4096 and registers2 will start from 8192. Make sure you add corresponding regdt for each register.  Shift can be changes by shiftR1 or shiftR2 parameter.
   if not mb then      require('genohm-scada.eibdgm')      require('luamodbus')          -- list of coil mapping, starting from 0      coils = { }              -- registers table 1 shift starting from 1          shiftR1 = 4095              -- list of register mapping, starting from 4096      registers1 = { '3/1/26', '3/1/29' }        -- list of register data types, element count must match registers table      regdt1 = { dt.int16, dt.int16 }                    -- registers table 2 shift starting from 1             shiftR2 = 8191           -- list of register mapping, starting from 8192      registers2 = { '3/1/32', '3/1/35' }        -- list of register data types, element count must match registers table      regdt2 = { dt.int16, dt.int16 }                        -- knx group write callback      function knxgroupwrite(event)        local value            -- try to find matching coil        for id, addr in ipairs(coils) do          if event.dst == addr then            value = knxdatatype.decode(event.datahex, dt.bool)            mb:setcoils(id - 1, value)          end        end            -- try to find matching register1        for id, addr in ipairs(registers1) do          if event.dst == addr then            value = knxdatatype.decode(event.datahex, regdt1[ id ])            mb:setregisters(id + shiftR1, value)          end        end             -- try to find matching register2        for id, addr in ipairs(registers2) do          if event.dst == addr then            value = knxdatatype.decode(event.datahex, regdt2[ id ])            mb:setregisters(id + shiftR2, value)          end        end          end          -- coil write callback      function mbwritecoils(coil, value)        local addr = coils[ coil + 1 ]        if addr then          grp.write(addr, value, dt.bool)        end      end          -- register write callback      function mbwriteregisters(register, value)        local addr1 = registers1[ register -shiftR1 ]            local addr2 = registers2[ register -shiftR2 ]        if addr1 then          grp.write(addr1, value, regdt1[ register - shiftR1])               elseif addr2 then          grp.write(addr2, value, regdt2[ register - shiftR2])        end      end              -- knx group monitor, handles group writes      knxclient = eibdgm:new({ timeout = 0.1 })      knxclient:sethandler('groupwrite', knxgroupwrite)          -- modbus slave, listen on all interfaces and default port 502      mb = luamodbus.tcp()      mb:open('0.0.0.0', 502)          -- setting slave id is optional      -- mb:setslave(1)          mb:setreceivetimeout(0.1)      mb:setmapping(#coils, 0, shiftR2 + 1 + #registers2, 0)          -- init coils      for id, addr in ipairs(coils) do        value = grp.getvalue(addr)        mb:setcoils(id - 1, value)      end          -- init registers1      for id, addr in ipairs(registers1) do        value = grp.getvalue(addr)        mb:setregisters(id + shiftR1, value)      end        -- init registers2      for id, addr in ipairs(registers2) do        value = grp.getvalue(addr)        mb:setregisters(id + shiftR2, value)      end          -- set callbacks for coil and register write      mb:setwritecoilcb(mbwritecoils)      mb:setwriteregistercb(mbwriteregisters)    end        -- handle modbus and knx    mb:handleslave()    knxclient:step()
