This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Paradox EVO192 integration
#1
The following scripts integrate Paradox EVO192 security panel. Paradox PRT3 printer module is used to connect the security panel to LM5 through RS232 serial port.
Thanks our forum member rebooter for contribution! Wink

guardZoneStatus library:


Code:
function guardzonefunction(zonenumber, zonestatus)
  guardZones = {
  [255255] = 'An empty zone has arrived',
  [01] = 'The main entrance. Motion Sensor.', 
  [02] = 'The cabinet. Motion Sensor.',
  [03] = 'The garage. Motion Sensor.',
  [04] = 'The stairs. Motion Sensor.',
  [05] = 'The living room. Motion Sensor.',
  [06] = 'The dining room. Motion Sensor.',
  [07] = 'The kitchen. Motion Sensor.',
  [08] = 'Garage entrance. Motion Sensor.',
  [09] = 'The main entrance. Window Break Sensor ',
  [10] = 'The cabinet. Window Break Sensor ',
  [11] = 'The garage. Window Break Sensor ',
  [13] = 'Living room. Window Break Sensor ',
  [14] = 'Dining room. Window Break Sensor ',
  [15] = 'The kitchen. Window Break Sensor ',
  [16] = 'The garage door. Reed switch ',
  [17] = 'The main entrance. Reed switch ',
  [18] = 'Dining room. Curtain',
  [19] = 'Boiler room. Motion Sensor.',
  [20] = 'The boiler room. Window jammer
  [21] = 'Cinema hall. Motion Sensor',
  [22] = 'Pantry. Motion Sensor',
  [24] = 'SPA room. Motion Sensor',
  [25] = 'Children's 1. Motion sensor',
  [26] = 'Hall 2 floor. Motion Sensor.',
  [27] = 'Children's 2. Motion sensor',
  [28] = 'Master bedroom. Motion Sensor',
  [30] = 'Pajar basement',
  [31] = 'Fire 1st floor',
  [32] = 'Fire 2nd floor',
  [33] = 'Fire Sauna',
  [34] = 'Fire attic',
  [35] = 'Server fire',
  [36] = 'Under the stairs',
  [50] = 'House is armed',
  [51] = 'House is disarmed',
}

-- Arming with mast
  zonename = guardZones[zonenumber]
-- log ("Zone Nr triggered: "..zonenumber.." status: "..zonestatus.." "..zonename)
-- log(zonename)
-- log(zonestatus)
-- log(guardZones[zonenumber])
  if zonestatus == 'closed' then
    status = 1
  elseif zonestatus == 'opened' then
    status = 0
  end

      if zonenumber == 1 then
            grp.update('8/0/1', status)
    elseif zonenumber == 2 then
--   zonename = guardZones[zonenumber]
          grp.update('8/0/2', status)
    elseif zonenumber == 3 then
          grp.update('8/0/3', status)
    elseif zonenumber == 4 then
          grp.update('8/0/4', status)
    elseif zonenumber == 5 then
          grp.update('8/0/5', status)
    elseif zonenumber == 6 then
          grp.update('8/0/6', status)
    elseif zonenumber == 7 then
          grp.update('8/0/7', status)
    elseif zonenumber == 8 then
          grp.update('8/0/8', status)
    elseif zonenumber == 9 then
          grp.update('8/0/9', status)
    elseif zonenumber == 10 then
          grp.update('8/0/10', status)
    elseif zonenumber == 11 then
          grp.update('8/0/11', status)
    elseif zonenumber == 13 then
          grp.update('8/0/13', status)
    elseif zonenumber == 14 then
          grp.update('8/0/14', status)
    elseif zonenumber == 15 then
          grp.update('8/0/15', status)
    elseif zonenumber == 16 then
          grp.update('8/0/16', status)
    elseif zonenumber == 17 then
          grp.update('8/0/17', status)
    elseif zonenumber == 18 then
          grp.update('8/0/18', status)
    elseif zonenumber == 19 then
          grp.update('8/0/19', status)
    elseif zonenumber == 20 then
          grp.update('8/0/20', status)
    elseif zonenumber == 21 then
          grp.update('8/0/21', status)
    elseif zonenumber == 22 then
          grp.update('8/0/22', status)
    elseif zonenumber == 24 then
          grp.update('8/0/24', status)
    elseif zonenumber == 25 then
          grp.update('8/0/25', status)
    elseif zonenumber == 26 then
          grp.update('8/0/26', status)
    elseif zonenumber == 27 then
          grp.update('8/0/27', status)
    elseif zonenumber == 28 then
          grp.update('8/0/28', status)
    elseif zonenumber == 30 then
          grp.update('8/0/30', status)
    elseif zonenumber == 31 then
          grp.update('8/0/31', status)
    elseif zonenumber == 32 then
          grp.update('8/0/32', status)
    elseif zonenumber == 33 then
          grp.update('8/0/33', status)
    elseif zonenumber == 34 then
          grp.update('8/0/34', status)
    elseif zonenumber == 35 then
          grp.update('8/0/35', status)
    elseif zonenumber == 36 then
          grp.update('8/0/36', status)

    -- process the status of security panel
    -- if armed then switch off lights in whole house
    elseif zonenumber == 50 then
    if grp.getvalue('0/5/8') == false then

      --    grp.update('0/5/5', status) --lights off
      grp.update('0/5/8', status) --security panel status
    end
   elseif zonenumber == 51 then
     if grp.getvalue('0/5/8') then

          grp.update('0/5/8', status) --security panel status
    end
    elseif zonenumber == 255255 then
    log("An empty zone has arrived")
    end --if zonenumber

end



RS232 communication script:

Code:
require('user.guardZoneStatus')

if not port then
  require('serial')
  port = serial.open('/dev/RS232', { baudrate = 9600, parity = 'none', databits = '8', stopbits = '1'})
  port:flush()
  line = ''
end

char = port:read(1, 1)
if char then
  if char == '\r' then
    line = line:trim()
    --log(line)

   -- mail('info@something.com', 'Installation X', line)

  --  loghex(line)
    zone = tonumber(string.sub(line,-2))

    if zone == nil  then
      zone = 255255
     -- log("An empty zone has arrived")
        end
--   if (zone > 1) or (zone <37 ) then

    if (string.match(line,'opened')) == ('opened') then
      zoneStatus = 'opened'
      armstatus = grp.getvalue('0/5/8') --reading current status of security system
-- log(armstatus)
    if armstatus == true then
    grp.update('0/5/8', false) -- write those which are not armed
    end

    else
      zoneStatus = 'closed'

    end -- string.match


      -- parsing logs for setting to alarm

      if (string.match(line,'Arming')) == ('Arming') then
        zoneStatus = 'closed'
        zone = 50
    --  elseif (string.match(line,'  in')) == ('  in') then
    --    zoneStatus = 'closed'
    --    zone = 50

    elseif (string.match(line,'ode entere')) == ('ode entere') then
        zoneStatus = 'opened'
          zone = 51

    end -- string.match

      guardzonefunction(zone,zoneStatus)
  --  end -- test for zone nember 1 - 36
    line = ''
  else
    line = line .. char
  end  -- if char '\r'
end
Reply
#2
Hello!

Here is my updated communication script. Maybe this helps someone...
It allows to see zone status, get info about areas (if there is trouble in some area and if area is open or not), arm/disarm etc...
Also it polls every minute area status.


Residential script (EVO192 communication, sleep interval 0 seconds):
Code:
require('user.guardZoneStatus')
require('user.guardAreaStatus')

if not port then
  require('serial')
  port = serial.open('/dev/RS232', { baudrate = 9600, parity = 'none', databits = '8', stopbits = '1'})
  port:flush()
  line = ''
end

control_house_security_ga = '10/1/0'                --area1 security status group address
control_woodstorage_security_ga = '10/1/1'    --area2 security status group address
security_code = '1234'

char = port:read(1, 1)
--log(char)
if char then
  if char == '\r' then
    line = line:trim()
    --log(line)
        event = string.sub(line,1,2)
   -- log(event)
    if event == 'G0' then
      eventnr = tonumber(string.sub(line,6,-5))
            area = tonumber(string.sub(line,10,-1))
      eventngr = tonumber(string.sub(line,2,4))
      if zone == nil  then
        zone = 255255
            end
      guardzonefunction(eventngr,eventnr,area)
    elseif event == 'RA' then
      area = tonumber(string.sub(line,3,5))
      securitystatus_1 = string.sub(line,6,6)
      areastatus_1 = string.sub(line,7,7)
      areastatus_2 = string.sub(line,8,8)
      areastatus_3 = string.sub(line,9,9)
      areastatus_4 = string.sub(line,10,10)
      areastatus_5 = string.sub(line,11,11)
      areastatus_6 = string.sub(line,12,12)
      guardareafunction(area,securitystatus_1,areastatus_1,areastatus_2,areastatus_3,areastatus_4,areastatus_5,areastatus_6  )
    end
    line = ''
  else
    line = line .. char
  end 
else
  request = grp.getvalue('32/5/0')    --scheduled script changes object to true every minute. !!!ADD SCHEDULED SCRIPT!!!
  if request then
    port:write('RA001\r')                --send area1 status request command
    os.sleep(0.5)
    port:write('RA002\r')                --send area2 status request command
    grp.update('32/5/0', false)
  end
  house_arm_disarm = grp.getvalue(control_house_security_ga)                        --1-Arm; 2-Force arm; 3-Stay arm; 4-Instant arm; 5-Disarm
  if house_arm_disarm == 1 then
    port:write('AA001A'..security_code..'\r')
    grp.update(control_house_security_ga, 0)
  elseif house_arm_disarm == 2 then
    port:write('AA001F'..security_code..'\r')
    grp.update(control_house_security_ga, 0)
  elseif house_arm_disarm == 3 then
    port:write('AA001S'..security_code..'\r')
    grp.update(control_house_security_ga, 0)
  elseif house_arm_disarm == 4 then
    port:write('AA001I'..security_code..'\r')
    grp.update(control_house_security_ga, 0)
  elseif house_arm_disarm == 5 then
    port:write('AD001'..security_code..'\r')
    grp.update(control_house_security_ga, 0)
  end
 
  woodstorage_arm_disarm = grp.getvalue(control_woodstorage_security_ga)    --1-Arm; 2-Force arm; 3-Stay arm; 4-Instant arm; 5-Disarm
  if woodstorage_arm_disarm == 1 then
    port:write('AA002A'..security_code..'\r')
    grp.update(control_woodstorage_security_ga, 0)
  elseif woodstorage_arm_disarm == 2 then
    port:write('AA002F'..security_code..'\r')
    grp.update(control_woodstorage_security_ga, 0)
  elseif woodstorage_arm_disarm == 3 then
    port:write('AA002S'..security_code..'\r')
    grp.update(control_woodstorage_security_ga, 0)
  elseif woodstorage_arm_disarm == 4 then
    port:write('AA002I'..security_code..'\r')
    grp.update(control_woodstorage_security_ga, 0)
  elseif woodstorage_arm_disarm == 5 then
    port:write('AD002'..security_code..'\r')
    grp.update(control_woodstorage_security_ga, 0)
  end
end

User library:

Script name: guardAreaStatus
Code:
function guardareafunction(areanumber, areastatus, areastatus1, areastatus2, areastatus3, areastatus4, areastatus5, areastatus6 ) --what must be process RA001DOONOOO; RA - Request area; 001 - Area number; D - Disarmed/Armed/Force armed/Stay armed/Instant armed; O - Zone in memory/Ok; O - Troube/Ok; N - Not ready/Ok; O - In programming/Ok; O - In alarm/Ok; O - Strobe/Ok

  house_area_status_ga = '10/0/0'
  woodstorage_area_status_ga = '10/0/1'
 
  house_area_trouble_ga = '10/3/0'
  woodstorage_area_trouble_ga = '10/3/1'
 
  house_area_not_ready_ga = '10/3/2'
  woodstorage_area_not_ready = '10/3/3'
 
  house_area_alarm_ga    = '10/2/0'
  woodstorage_area_alarm_ga = '10/2/1'
 
  if areastatus == 'D' then
    if areanumber == 1 then
      grp.write(house_area_status_ga, 0)
    elseif areanumber == 2 then
      grp.write(woodstorage_area_status_ga, 0)
    end
  elseif areastatus == 'A' then
    if areanumber == 1 then
        grp.update(house_area_status_ga, 1)
    elseif areanumber == 2 then
      grp.update(woodstorage_area_status_ga, 1)
    end
  elseif areastatus == 'F' then
    if areanumber == 1 then
        grp.update(house_area_status_ga, 2)
    elseif areanumber == 2 then
      grp.update(woodstorage_area_status_ga, 2)
    end
  elseif areastatus == 'S' then
    if areanumber == 1 then
        grp.update(house_area_status_ga, 3)
    elseif areanumber == 2 then
      grp.update(woodstorage_area_status_ga, 3)
    end
  elseif areastatus == 'I' then
    if areanumber == 1 then
        grp.update(house_area_status_ga, 4)
    elseif areanumber == 2 then
      grp.update(woodstorage_area_status_ga, 4)
    end
  end
 
  if areastatus2 == 'T' then
    if areanumber == 1 then
      grp.update(house_area_trouble_ga, true)
    elseif areanumber == 2 then
      grp.update(woodstorage_area_trouble_ga, true)
    end
  elseif areastatus2 == 'O' then
    if areanumber == 1 then
      grp.update(house_area_trouble_ga, false)
    elseif areanumber == 2 then
      grp.update(woodstorage_area_trouble_ga, false)
    end
  end
 
  if areastatus3 == 'N' then
    if areanumber == 1 then
      grp.update(house_area_not_ready_ga, true)
    elseif areanumber == 2 then
      grp.update(woodstorage_area_not_ready, true)
    end
  elseif areastatus3 == 'O' then
    if areanumber == 1 then
      grp.update(house_area_not_ready_ga, false)
    elseif areanumber == 2 then
      grp.update(woodstorage_area_not_ready, false)
    end
  end
 
  if areastatus5 == 'A' then
    if areanumber == 1 then
      grp.update(house_area_alarm_ga, true)
    elseif areanumber == 2 then
      grp.update(woodstorage_area_alarm_ga, true)
    end
  elseif areastatus5 == 'O' then
    if areanumber == 1 then
      grp.update(house_area_alarm_ga, false)
    elseif areanumber == 2 then
      grp.update(woodstorage_area_alarm_ga, false)
    end
  end
 
end
Script name: guardZoneStatus

Code:
function guardzonefunction( eventgroup,eventnumber,areanumber)
  guardZones = {
  [255255] = 'An empty zone has arrived',
  [01] = 'Tehnoruum PIR.', 
  [02] = '1k Trepihall PIR.',
  [03] = 'Kontor PIR.',
  [04] = 'Esik PIR.',
  [05] = 'Elutuba PIR.',
  [06] = 'Magamistuba PIR.',
  [07] = 'Garderoob PIR.',
  [08] = 'Kuur PIR.',
  [09] = 'Mona PIR ',
  [10] = 'Cara PIR  ',
  [11] = '2k Trepihall PIR ',
  [12] = 'Tehnoruumi Suits ',   
  [13] = '1 Trepihall Suit ',
  [14] = 'Kontori Suits ',
  [15] = 'Esiku Suits ',
  [16] = 'Elutoa Suits ',
  [17] = 'Magamistoa Suits ',
  [18] = 'Garderoob Suits',
  [19] = 'Mona Suits',
  [20] = 'Cara Suits',
  [21] = '2 Trepihall Suit',
  [22] = '2k Elutoa Suits',
  [23] = 'Kuuri Uks',
  [24] = 'Kontori Aken',
  [25] = 'Peauks',
  [26] = 'Köögi Aken.',
  [27] = 'Terrassi Uks',
  [28] = '1k Vannitoa Uks',
  [29] = '1k Vannitoa Aken',
  [30] = 'Magamistoa Aken',
  [31] = 'Kuuri Aken',
  [32] = 'Mona 1 Aken',
  [33] = 'Cara 1 Aken',
  [34] = '2k Vannitoa Aken',
  [35] = '2k Elutuba M',
  [36] = 'Mona 2 Aken',
  [37] = 'Cara 2 Aken',
  [38] = 'Valvekilp',

}

  house_area_status_ga = '10/0/0'
  woodstorage_area_status_ga = '10/0/1'
 
  house_area_alarm_ga    = '10/2/0'
  woodstorage_area_alarm_ga = '10/2/1'
 
  house_area_exit_delay_ga = '10/0/2'
  house_area_entry_delay_ga = '10/0/3'
 
  woodstorage_area_exit_delay_ga = '10/0/4'
  woodstorage_area_entry_delay_ga = '10/0/5'

  if eventgroup == 0 or eventgroup == 1 then
    if eventgroup == 0 then
      grp.update('10/4/'..eventnumber, false)
    elseif eventgroup == 1 then
      grp.update('10/4/'..eventnumber, true)
    end
  elseif eventgroup == 13 then
    if areanumber == 1 then
      grp.update(house_area_status_ga, 0)
    elseif areanumber == 2 then
      grp.update(woodstorage_area_status_ga, 0)
    end
  elseif eventgroup == 64 then
    if eventnumber == 0 then
      if areanumber == 1 then
        grp.update(house_area_status_ga, 1)
      elseif areanumber == 2 then
        grp.update(woodstorage_area_status_ga, 1)
      end
    elseif eventnumber == 1 then
      if areanumber == 1 then
        grp.update(house_area_status_ga, 2)
      elseif areanumber == 2 then
        grp.update(woodstorage_area_status_ga, 2)
      end
    elseif eventnumber == 2 then
      if areanumber == 1 then
        grp.update(house_area_status_ga, 3)
      elseif areanumber == 2 then
        grp.update(woodstorage_area_status_ga, 3)
      end
    elseif eventnumber == 3 then
      if areanumber == 1 then
        grp.update(house_area_status_ga, 4)
      elseif areanumber == 2 then
        grp.update(woodstorage_area_status_ga, 4)
      end
    elseif eventnumber == 4 or eventnumber == 5 or eventnumber == 6 or eventnumber == 7 then
      if areanumber == 1 then
        grp.update(house_area_alarm_ga, true)
      elseif areanumber == 2 then
        grp.update(woodstorage_area_alarm_ga, true)
      end
    end
  elseif eventgroup == 65 then
    if eventnumber == 1 then
      if areanumber == 1 then
        grp.update(house_area_exit_delay_ga, true)
      elseif areanumber == 2 then
        grp.update(woodstorage_area_exit_delay_ga, true)
      end
    elseif eventnumber == 2 then
      if areanumber == 1 then
        grp.update(house_area_entry_delay_ga, true)
      elseif areanumber == 2 then
        grp.update(woodstorage_area_entry_delay_ga, true)
      end
    elseif eventnumber == 0 then
      if areanumber == 1 then
        grp.update(house_area_entry_delay_ga, false)
        grp.update(house_area_exit_delay_ga, false)
      elseif areanumber == 2 then
        grp.update(woodstorage_area_entry_delay_ga, false)
        grp.update(woodstorage_area_exit_delay_ga, false)
      end
    end
  end
end
Resident script for communication check (EVO192 Communication check, sleep interval 10s):

Code:
last_timestamp = grp.find("10/0/0").updatetime --Area1 status (status is polled every minute from security system)
communication_error = grp.getvalue('10/3/4')

now = os.microtime()

if (now - last_timestamp) >= 120 then --if object hasn't updated on last 120s then generate communication error
  if communication_error == false then
    grp.update('10/3/4', true)
  end
else
  if grp.getvalue('10/3/4')==true then
    grp.update('10/3/4', false)
  end
end

Here is UI:
       
Reply
#3
Another update to get integration done about 1 minute.

Now my script reads out all arealabels and zone labels (You don't need to know anything about EVO program). Also creates automatically group objects. I tested it couple days ago in my new project and really, integration takes about 1-2 minutes.  Cool
What you probably need to do is edit zone labels to more understandable form (paradox allows enter only 16 characters for area and zone name).

Program needs one main group address range (example 10/x/x)

Group address structure is like this:
Code:
security_main_ga = '10/' --'3-level' = main/middle/sub. Make sure that 10/0/0 - 10/7/X group addresses are not used. System creates objects automatically.

10/0/1 - Area 1 security status [0-DISARMED, 1-ARMED, 2-FORCE ARMED, 3-STAY ARMED, 4-INSTANT ARMED]
...
10/0/8 - Area 8 security status


10/0/11 - Area 1 exit delay    
...
10/0/18 - Area 8 exit delay


10/0/21 - Area 1 entry delay
...
10/0/28 - Area 8 entry delay


10/0/31 - Area 1 alarm status
...
10/0/38 - Area 8 alarm status


10/0/41 - Area 1 trouble
...
10/0/48 - Area 8 trouble


10/0/51 - Area 1 not ready
...
10/0/58 - Area 8 not ready


10/1/1 - Area 1 control        [1-ARM, 2-FORCE ARM, 3-STAY ARM, 4-INSTANT ARM, 5-DISARM]
...
10/1/8 - Area 8 control


10/2/1 - Zone 1 status
...
10/2/xxx - Zone xxx status

All what you need to change is in resident script (group addresses).

Resident script (EVO192 communication, sleep interval 0):
Code:
require('user.guardZoneStatus')
require('user.guardAreaStatus')
require('user.guardAreaLabels')
require('user.guardZoneLabels')
command_enum = {
  [1] = 'A', 
  [2] = 'F',
  [3] = 'S',
  [4] = 'I',
}
if not port then
  require('serial')
  port = serial.open('/dev/RS232', { baudrate = 9600, parity = 'none', databits = '8', stopbits = '1'})
  port:flush()
  line = ''
end
security_main_ga = '10/'           --'3-level' = main/middle/sub. Make sure that 10/0/0 - 10/7/X group addresses are not used. System creates objects automatically.
security_code = '1234'
request_area_status_ga = '32/5/0'  --Create scheduled script for this one. Write true every minute.
request_zone_labels_ga = '32/5/3'  --You need to change this to true only one time or if security zones are changed.
                                   --This also activates group address generation.
                                   --Make sure that zone label is not "Zone 001, Zone 002 etc because these zone names gonna be ignored.
request_area_labels_ga = '32/5/4'  --You need to change this to true only one time or if security areas are changed.
                                   --This also activates group address generation.
                                   --Make sure that area label is not "Area 001, Area 002 etc because these area names gonna be ignored.

request_zone_name_count = 50       --how many zones will be scanned to get zone labels.
active_areas = 1                   --How many areas are polled periodically. Starts on first area.
char = port:read(1, 1)
--log(char)
if char then
  if char == '\r' then
    line = line:trim()
    log(line)
        event = string.sub(line,1,2)
   -- log(event)
    if event == 'G0' then
      eventnr = tonumber(string.sub(line,6,-5))
            area = tonumber(string.sub(line,10,-1))
      eventngr = tonumber(string.sub(line,2,4))
      guardzonefunction(eventngr,eventnr,area,security_main_ga)
    elseif event == 'RA' then
      area = tonumber(string.sub(line,3,5))
      securitystatus_1 = string.sub(line,6,6)
      areastatus_1 = string.sub(line,7,7)
      areastatus_2 = string.sub(line,8,8)
      areastatus_3 = string.sub(line,9,9)
      areastatus_4 = string.sub(line,10,10)
      areastatus_5 = string.sub(line,11,11)
      areastatus_6 = string.sub(line,12,12)
      guardareafunction(area,securitystatus_1,areastatus_1,areastatus_2,areastatus_3,areastatus_4,areastatus_5,areastatus_6,security_main_ga  )
    elseif event == 'AL' then
      area = tonumber(string.sub(line,3,5))
      name = string.sub(line,6,16)
      guardarealabelfunction(area, name,security_main_ga)
    elseif event == 'ZL' then
      zone = tonumber(string.sub(line,3,5))
      name = string.sub(line,6,16)
      guardzonelabelfunction(zone, name,security_main_ga)
    end
    line = ''
  else
    line = line .. char
  end 
else
  request = grp.getvalue(request_area_status_ga)    --scheduled script changes object to true every minute
  if request then
    for i = 1, active_areas, 1 do
            port:write('RA00'.. i .. '\r')                --send area1 status request command
        os.sleep(0.2)
      if i==active_areas then
            grp.update(request_area_status_ga, false)
      end
    end
  end
 
  request_area_names = grp.getvalue(request_area_labels_ga)
  if request_area_names then
    for i = 1, 8, 1 do
        port:write('AL00'..tostring(i)..'\r')
        os.sleep(0.2)
    end
      grp.update(request_area_labels_ga, false)
  end
 
  request_zone_names = grp.getvalue(request_zone_labels_ga)
  if request_zone_names then
    for i = 1, request_zone_name_count, 1 do
      if i<10 then
          port:write('ZL00'..tostring(i)..'\r')
          os.sleep(0.2)
      else
        port:write('ZL0'..tostring(i)..'\r')
          os.sleep(0.2)
      end
    end
  grp.update(request_zone_labels_ga, false)
  end
  for i = 1, active_areas, 1 do
    exist = grp.alias(security_main_ga .. '1/' .. i)
      if exist ~= nil then
      AreaControl = grp.getvalue(security_main_ga .. '1/' .. i)     --1-Arm; 2-Force arm; 3-Stay arm; 4-Instant arm; 5-Disarm
      if AreaControl ~=0 then
        if AreaControl ~= 5 then
          port:write('AA00' .. i .. command_enum[AreaControl] .. security_code ..'\r')
          grp.update(security_main_ga .. '1/' .. i, 0)
        else
          port:write('AD00' .. i .. security_code ..'\r')
          grp.update(security_main_ga .. '1/' .. i, 0)
          end
          end
    end
    end
end

User library (guardAreaLabels):
Code:
function guardarealabelfunction(areanumber, areaname, security_main_ga) 
 
  if areaname ~= ('Area ' .. tonumber(areanumber)) then
    for i = 1, 7, 1 do
      if i==1 then
        exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber))
        if exist == nil then
          address = grp.create({
            datatype = dt.uint8,
            address = security_main_ga .. '0/' .. tonumber(areanumber),
              name = areaname .. ' security status',
            comment = 'Automatically created object - Security Area '.. tonumber(areanumber),
            units = '',
            tags = { },
          })
        end
      elseif i==2 then
        exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+10)
        if exist == nil then
          address = grp.create({
            datatype = dt.bool,
            address = security_main_ga .. '0/' .. tonumber(areanumber)+10,
              name = areaname .. ' exit delay',
              comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' exit delay',
            units = '',
            tags = { },
          })
        end
      elseif i==3 then
        exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+20)
        if exist == nil then
          address = grp.create({
            datatype = dt.bool,
            address = security_main_ga .. '0/' .. tonumber(areanumber)+20,
              name = areaname .. ' entry delay',
              comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' entry delay',
            units = '',
            tags = { },
          })
        end
      elseif i==4 then
        exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+30)
        if exist == nil then
          address = grp.create({
            datatype = dt.bool,
            address = security_main_ga .. '0/' .. tonumber(areanumber)+30,
              name = areaname .. ' alarm status',
              comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' alarm status',
            units = '',
            tags = { },
          })
        end
      elseif i==5 then
        exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+40)
        if exist == nil then
          address = grp.create({
            datatype = dt.bool,
            address = security_main_ga .. '0/' .. tonumber(areanumber)+40,
              name = areaname .. ' trouble',
              comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' trouble',
            units = '',
            tags = { },
          })
        end
      elseif i==6 then
        exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+50)
        if exist == nil then
          address = grp.create({
            datatype = dt.bool,
            address = security_main_ga .. '0/' .. tonumber(areanumber)+50,
              name = areaname .. ' not ready',
              comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' not ready',
            units = '',
            tags = { },
          })
        end
      elseif i==7 then
        exist = grp.alias(security_main_ga .. '1/' .. tonumber(areanumber))
        if exist == nil then
          address = grp.create({
            datatype = dt.uint8,
            address = security_main_ga .. '1/' .. tonumber(areanumber),
              name = 'Control ' .. areaname,
              comment = 'Automatically created object - Control Security Area '.. tonumber(areanumber),
            units = '',
            tags = { },
          })
        end
      end
    end
  end
end

User library (guardAreaStatus):
Code:
function guardareafunction(areanumber, areastatus, areastatus1, areastatus2, areastatus3, areastatus4, areastatus5, areastatus6, security_main_ga ) --what must be process RA001DOONOOO; RA - Request area; 001 - Area number; D - Disarmed/Armed/Force armed/Stay armed/Instant armed; O - Zone in memory/Ok; O - Troube/Ok; N - Not ready/Ok; O - In programming/Ok; O - In alarm/Ok; O - Strobe/Ok
 
  if areastatus == 'D' then
    grp.write(security_main_ga .. '0/' .. areanumber , 0)
  elseif areastatus == 'A' then
    grp.update(security_main_ga .. '0/' .. areanumber , 1)
  elseif areastatus == 'F' then
    grp.update(security_main_ga .. '0/' .. areanumber , 2)
  elseif areastatus == 'S' then
    grp.update(security_main_ga .. '0/' .. areanumber , 3)
  elseif areastatus == 'I' then
    grp.update(security_main_ga .. '0/' .. areanumber , 4)
  end
 
  if areastatus2 == 'T' then
    grp.update(security_main_ga .. '0/' .. areanumber+40 , true)
  elseif areastatus2 == 'O' then
    grp.update(security_main_ga .. '0/' .. areanumber+40 , false)
  end
 
  if areastatus3 == 'N' then
    grp.update(security_main_ga .. '0/' .. areanumber+50 , true)
  elseif areastatus3 == 'O' then
    grp.update(security_main_ga .. '0/' .. areanumber+50 , false)
  end
 
  if areastatus5 == 'A' then
    grp.update(security_main_ga .. '0/' .. areanumber+30 , true)
  elseif areastatus5 == 'O' then
    grp.update(security_main_ga .. '0/' .. areanumber+30 , false)
  end
end

User library (guardZoneLabels):
Code:
function guardzonelabelfunction(zonenumber, zonename, security_main_ga)
 
  exist = grp.alias(security_main_ga .. '2/'.. tonumber(zonenumber))
  if exist == nil then
    if zonenumber<10 then
      if zonename ~= ('Zone 00' .. tonumber(zonenumber)) then
        address = grp.create({
          datatype = dt.bool,
          address = security_main_ga .. '2/'.. tonumber(zonenumber),
          name = zonename,
            comment = 'Automatically created object - Zone '.. tonumber(zonenumber),
          units = '',
          tags = { },
        })
      end
    elseif zonenumber>=10 and zonenumber<100 then
      if zonename ~= ('Zone 0' .. tonumber(zonenumber)) then
        address = grp.create({
          datatype = dt.bool,
          address = security_main_ga .. '2/'.. tonumber(zonenumber),
          name = zonename,
            comment = 'Automatically created object - Zone '.. tonumber(zonenumber),
          units = '',
          tags = { },
        })
      end
    elseif zonenumber>=100 then
      if zonename ~= ('Zone ' .. tonumber(zonenumber)) then
        address = grp.create({
          datatype = dt.bool,
          address = security_main_ga .. '2/'.. tonumber(zonenumber),
          name = zonename,
            comment = 'Automatically created object - Zone '.. tonumber(zonenumber),
          units = '',
          tags = { },
        })
      end
    end
  end
end

User library (guardZoneStatus):
Code:
function guardzonefunction( eventgroup,eventnumber,areanumber,security_main_ga)

  if eventgroup == 0 or eventgroup == 1 then
    if eventgroup == 0 then
      grp.update(security_main_ga .. '2/'..eventnumber, false)
    elseif eventgroup == 1 then
      grp.update(security_main_ga .. '2/'..eventnumber, true)
    end
  elseif eventgroup == 5 then -- disarm
    grp.update(security_main_ga .. '0/' .. areanumber , 0)
    grp.update(security_main_ga .. '0/' .. areanumber+10,false)         --reset exit delay
    grp.update(security_main_ga .. '0/' .. areanumber+20 , false)        --reset entry delay
  elseif eventgroup == 13 then -- disarm
    grp.update(security_main_ga .. '0/' .. areanumber , 0)
    grp.update(security_main_ga .. '0/' .. areanumber+10,false)         --reset exit delay
    grp.update(security_main_ga .. '0/' .. areanumber+20 , false)        --reset entry delay
  elseif eventgroup == 64 then --
    if eventnumber == 0 then
        grp.write(security_main_ga .. '0/' .. areanumber , 1)
      grp.update(security_main_ga .. '0/' .. areanumber+10,false)         --reset exit delay
        grp.update(security_main_ga .. '0/' .. areanumber+20 , false)        --reset entry delay
    elseif eventnumber == 1 then
      grp.write(security_main_ga .. '0/' .. areanumber , 2)
      grp.update(security_main_ga .. '0/' .. areanumber+10,false)         --reset exit delay
        grp.update(security_main_ga .. '0/' .. areanumber+20 , false)        --reset entry delay
    elseif eventnumber == 2 then
      grp.write(security_main_ga .. '0/' .. areanumber , 3)
      grp.update(security_main_ga .. '0/' .. areanumber+10,false)         --reset exit delay
        grp.update(security_main_ga .. '0/' .. areanumber+20 , false)        --reset entry delay
    elseif eventnumber == 3 then
     grp.write(security_main_ga .. '0/' .. areanumber , 4)
      grp.update(security_main_ga .. '0/' .. areanumber+10,false)         --reset exit delay
        grp.update(security_main_ga .. '0/' .. areanumber+20 , false)        --reset entry delay
    elseif eventnumber == 4 or eventnumber == 5 or eventnumber == 6 or eventnumber == 7 then
      grp.update(security_main_ga .. '0/' .. areanumber+30 , true)
    end
  elseif eventgroup == 65 then
    if eventnumber == 1 then
      grp.update(security_main_ga .. '0/' .. areanumber+10 , true)
    elseif eventnumber == 2 then
      grp.update(security_main_ga .. '0/' .. areanumber+20 , true)
    elseif eventnumber == 0 then
      grp.update(security_main_ga .. '0/' .. areanumber+10 , false)
      grp.update(security_main_ga .. '0/' .. areanumber+20 , false)
    end
  end
end

After you request area and zone names, give it some time to scan and create group objects. Mine needed about 15-20 seconds (1 area, 50 zones)...

All objects what are created automatically they have also object comment "Automatically created object - Security Area X", "Automatically created object - Zone XX" etc..
Reply
#4
Hi, thank you for this script! I'm investigating the best possible way to integrate a security system with KNX in my next project. Satel has INT-KNX-2, which is great, but it has certain limitations (e.g. only 64 addresses). There are some pricey 3rd party modules for DSC. And there is Paradox with PRT3 and pricey 3rd party modules again, or using Logic Machine alternatively. The last option I like the most, because I'll probably put a Logic Machine into the project anyways.

Two questions:
1. Does this script work with the newer Paradox serial module? PRT3 is now discontinued and replaced.
2. Are zone changes reported imidiately? For example if a motion sensor detects motion, is this reported on the same second?
Reply
#5
(01.12.2020, 21:05)mishoboss Wrote: Hi, thank you for this script! I'm investigating the best possible way to integrate a security system with KNX in my next project. Satel has INT-KNX-2, which is great, but it has certain limitations (e.g. only 64 addresses). There are some pricey 3rd party modules for DSC. And there is Paradox with PRT3 and pricey 3rd party modules again, or using Logic Machine alternatively. The last option I like the most, because I'll probably put a Logic Machine into the project anyways.

Two questions:
1. Does this script work with the newer Paradox serial module? PRT3 is now discontinued and replaced.
2. Are zone changes reported imidiately? For example if a motion sensor detects motion, is this reported on the same second?

Hi!

I definitelly should choose LM to integrate security system. You have no limits when using LM. Can program whatever you want. 

Answers:
1. I havent tested it but if all commands are the same then it will work.
2. Yes, this is realtime info. In one project I am using movement from security as triger and switch lights when brightness is below setpoint.
Reply
#6
Hi, is there a way to control Paradox PGMs (outputs)?
Reply
#7
(26.06.2021, 05:27)mishoboss Wrote: Hi, is there a way to control Paradox PGMs (outputs)?

I didn't find any straight solution because there is no command to control PGM output directly. PGM output is meant to control via some statements inside paradox.

But, this solution should work (haven't tested it by myself) but paradox uses this solution with RF remotes.
You can try to use utility key and create this kind of configuration (picture 1 attached). I think there is possible to create similar configuration in BabyWare also.

In LM add this code in residential script to test it out:

Code:
  utility_key1_grp_addr = 'x/x/x' -- turn PGM on group address
  utility_key2_grp_addr = 'x/x/x' -- turn PGM off group address

  utility_key1 = grp.getvalue(utility_key1_grp_addr) -- PGM on
  utility_key2 = grp.getvalue(utility_key2_grp_addr) -- PGM off
 
  if utility_key1==true or utility_key1==1 then
     port:write('UK001\r')
     grp.update(utility_key1_grp_addr, false)
     os.sleep(0.2)
  elseif utility_key2==true or utility_key2==1 then
     port:write('UK002\r')
     grp.update(utility_key2_grp_addr, false)
     os.sleep(0.2)
  end

enable log(event) in residential script to see if command is accepted.

Unfortunately there is no request/status command to see what is PGM state.

Hope this helps.

Attached Files Thumbnail(s)
   
Reply
#8
Hello. Everything is perfect but I see that the connection is through RS-232 port. My initial question is if there is some possibility to manage a alarm central through http connection. This kind of central usually include web server.
Thank you.
Reply
#9
Hi!

Thanks for your work, @fleeceable! If I can make this work it would save me a lot of work Smile

For now I'm receiving only nill and a <?> character as you can see in the attachment.

I think the problem may be in the PTR3 options. Can you please give me some pointers how to solve this?


BR,
André Neves

Attached Files Thumbnail(s)
       
Reply
#10
Check the baudrate settings. All examples here use 9600, but your device is set to 19200.
Reply
#11
(22.02.2022, 12:09)admin Wrote: Check the baudrate settings. All examples here use 9600, but your device is set to 19200.

Hi,

It is at 9600. I just made the print after a test at 19200.
Reply
#12
ASCII protocol should only contain printable characters. Since you are getting <?> (unprintable character) it means that there's something wrong on the communication level.
Reply
#13
You can also try to switch Tx and Rx cables on logic side.
Another way to test that your PRT3 module (and paradox program) works is to use RS232 to USB converter and connect PRT3 to computer. Then use Docklight (https://docklight.de/) program. If all settings are correct you should see some data on Docklight terminal...

I have used that Logic library on 4 sites and all works great.
Reply
#14
(11.03.2022, 11:51)fleeceable Wrote: You can also try to switch Tx and Rx cables on logic side.
Another way to test that your PRT3 module (and paradox program) works is to use RS232 to USB converter and connect PRT3 to computer. Then use Docklight (https://docklight.de/) program. If all settings are correct you should see some data on Docklight terminal...

I have used that Logic library on 4 sites and all works great.

Problem solved!

It was a bad wire connection inside the DB9 connector. The gnd wire was disconected.

This library is great and helped a lot. THanks.
Reply
#15
(18.07.2020, 14:37)fleeceable Wrote: ..

Nice work! Thanks... 
Unfortunatelly PRP3 ASCII Protocol missing a way to bypass zones Sad
Reply
#16
It is hard to understand why Paradox did not include Bypass function on the PRT3.
They have it with the IP module... Everyone should send an update request to Paradox to have it added to the PRT3. It takes numbers to get results.
Reply
#17
Hi! Right now the D (disarmed) status is mapped to number 0 and the disarm control is mapped to number 5. I need disarm control and status to be mapped to the same number, for example 5. So I thought it would be easy to remap those here:

if areastatus == 'D' then
grp.update(security_main_ga .. '0/' .. areanumber , 5)
elseif areastatus == 'A' then
grp.update(security_main_ga .. '0/' .. areanumber , 1)
elseif areastatus == 'F' then
grp.update(security_main_ga .. '0/' .. areanumber , 2)
elseif areastatus == 'S' then
grp.update(security_main_ga .. '0/' .. areanumber , 3)
elseif areastatus == 'I' then
grp.update(security_main_ga .. '0/' .. areanumber , 4)
end

And added the fifth option here:


command_enum = {
[1] = 'A',
[2] = 'F',
[3] = 'S',
[4] = 'I',
[5] = 'D',
}

However DISARMED status is still reported as 0 instead of 5 right after disarming, or it's even not reported at all in some cases. I've scheduled a script to call request_area_status_ga = true every minute and this one successfully updates it to 5. So it works, just not right after DISARMING for some reason. All other controls successfully update the status, it's just the disarm one that is the issue. What I'm missing here?
Reply
#18
Are you overriding existing object or did you create virtual status?
------------------------------
Ctrl+F5
Reply
#19
(22.04.2024, 08:47)mishoboss Wrote: Hi! Right now the D (disarmed) status is mapped to number 0 and the disarm control is mapped to number 5. I need disarm control and status to be mapped to the same number, for example 5. So I thought it would be easy to remap those here:

if areastatus == 'D' then
    grp.update(security_main_ga .. '0/' .. areanumber , 5)
  elseif areastatus == 'A' then
    grp.update(security_main_ga .. '0/' .. areanumber , 1)
  elseif areastatus == 'F' then
    grp.update(security_main_ga .. '0/' .. areanumber , 2)
  elseif areastatus == 'S' then
    grp.update(security_main_ga .. '0/' .. areanumber , 3)
  elseif areastatus == 'I' then
    grp.update(security_main_ga .. '0/' .. areanumber , 4)
  end

And added the fifth option here:


command_enum = {
  [1] = 'A', 
  [2] = 'F',
  [3] = 'S',
  [4] = 'I',
  [5] = 'D',
}

However DISARMED status is still reported as 0 instead of 5 right after disarming, or it's even not reported at all in some cases. I've scheduled a script to call request_area_status_ga = true every minute and this one successfully updates it to 5. So it works, just not right after DISARMING for some reason. All other controls successfully update the status, it's just the disarm one that is the issue. What I'm missing here?

You need to change this to get 5 for disarm:

user.guardZoneStatus
Code:
  elseif eventgroup == 5 then -- user code entered on keypad
    grp.update(security_main_ga .. '0/' .. areanumber , 0) ------<<<<<CHANGE THIS TO 5
    grp.update(security_main_ga .. '0/' .. areanumber+10,false)         --reset exit delay
    grp.update(security_main_ga .. '0/' .. areanumber+20 , false)        --reset entry delay
  elseif eventgroup == 13 or  eventgroup == 14  then -- disarm with master or user code
    grp.update(security_main_ga .. '0/' .. areanumber , 0) ------<<<<<CHANGE THIS TO 5
    grp.update(security_main_ga .. '0/' .. areanumber+10,false)         --reset exit delay
    grp.update(security_main_ga .. '0/' .. areanumber+20 , false)        --reset entry delay

Also you don't need to change  "command_enum" because that is used only to send right arming command (usual arm, force arm, stay arm etc). If AreaControl variable is 5 then it gonna disarm on either way. Check residential script line 104.
Reply