Hi,
need a little explanation from more experienced persons.
I use LM like Modbus TCP slave device. I need read/write over it to KNX devices. All was done fine and works, till I need to add one more, 12th knx thermostat.
I used 124 registers. When I added new device and add registers, I found out I cannot read over 125 register or write over 123.. Is possible to solve somehow this problem? At scanner max 125 registers (picture below), and I cannot read as example register 126..
BR,
Alex